Motor makes lights dim

I got an Air Compressor in my garage. It's just a small household type, not the large ones used in service garages. The motor is free, and turns easily by hand. The other day I plugged it in and had to fill a tire. It started, but would quit running for a few seconds then go again. At the time I thought the pressure control was dying that turns it off and on, but it did finally pump up to full pressure.

Today I plugged it in again, and the motor will not start. It hums, but will not start at all. The weird part is that all the lights in the garage get very dim, which includes the compact florescents in the ceiling lights, and the 100W indecesant flood light outside. What is even more strange, is the fact that the breakers do not trip, even after leaving it plugged in for approx. one minute. What the heck is going on?

Note, the motor is a 1/3HP 120V capacitor start motor. The wiring in the garage is all new as of one year ago. The lights are on a different circuit than the compressor outlet, which is mounted directly below the breaker box, and has its own 20A breaker. Therefore, I can be sure the wiring is not at fault. Just for the heck of it, I have an outdoor receptacle on a GFCI. I plugged the compressor into that outlet, and the GFCI did not trip either.

I have done wiring and electrical stuff for many years, and this one is just too weird....... All I can figure is that the capacitor is bad, but I'd still think the breaker would trip.

Anyone got any ideas?

PS. My 240V well pump also runs off the garage panel, and works fine.

Mark

Reply to
maradcliff
Loading thread data ...

This is Turtle.

Change out the ITE breaker and get a new one and check the motor bearings out on the air compressor for they maybe getting bad. Yes i said change out your ITE breaker out !

TURTLE

Reply to
TURTLE
040911 0212 - snipped-for-privacy@UNLISTED.com posted:

Sounds like the motor start switch contact is pitted and not making connection anymore. Take the motor apart and the centrifugal switch is inside one of the end covers. Clean the contacts, if possible -- sometimes they are so pitted that they must be replaced -- and then put the whole thing back together again.

Reply to
indago

Have you drained the tank recently ? The compressor could be so full now it's hydro locking.

Bill

Reply to
berkshire bill

I have Cutler Hammer breakers in there. You must know about a problems with ITE breakers????

However, I went in the garage to saw a board and the saw would not run at full speed, and the lights all went very dim. That clued me there is another problem, and in the wiring, not the motor. Since the water pump is OK, that means I must have a bad neutral. Just for the heck of it, I plugged in a spare 1/2HP motor. The lights inside the garage went OUT. The floodlight on the outside of the garage BURNED OUT.

The wiring in the garage is new, but I opened the breaker box and everything is tight and looks fine. I suspect the overhead wires from the main pole to the garage are at fault. This is a farm. The house barn, and another shed are all OK. They all have a separate overhead line from the main pole, except the house which is underground. There has got to be a bad neutral connection overhead. I looked up there with a flashlight (it's nighttime). All wires are physically connected, but one of the neutrals has got to have a bad connection. I have to wait until daytime to go up there. Not what I didn't want to do today. I hate going up on poles anytime. I am no fan of heights, especially on ladders against round poles. I have a feeling I have no neutral at all, just the ground rod is giving me enough ground to light the lightbulbs.

PS. Just for the heck of it, I just went outside and ran my 100 foot extension cord from that other shed to the garage, and the air compressor works just fine.

Mark

Reply to
maradcliff

That is a good suggestion, but I took the belt off and it still did not run. If you read my other recent post, I suspect I have a missing overhead neutral. Now if I can only figure out where !!!!

Thanks

Mark

Reply to
maradcliff

Could it be that if you look at the 1/3 hp motor nameplate for LR= Locked Rotor current, its probably around 16 amps ,, maybe that's why its not tripping the breaker quickly.

Reply to
bumtracks

I doubt you are missing a neutral. Try plugging the motor someplace else in the house on a different circuit. Same thing?

I suspend the motor bearings are going. Since there is a strong load, but no short, the breaker will not pop. As long as the load is less than the breaker rating, it will hold but cause lights to dim.

Did you spin the motor by hand? That will give you a clue. Could be a few other things also. as was already pointed out. Ed

Reply to
Edwin Pawlowski

I think you are on the right track. If you have a breaker panel right there and lights on other circuits are dimming, or worse, you have a bad connection somewhere. Greg

Reply to
Greg O

Ed, I think he is on the right track, there is a bad connection somewhere. With the poor neutral the voltage drops on the 120 volt circuits that causes the amps to drop also, less voltage to push = less amp draw, so the breakers hold. Why would lighting on a differant circuit on the same panel dim or go out when the motor starts? A 1/3 HP motor should not cause much more than a flicker in the lights when stalled. I would try the compressor off the house panel for kicks before going crazy, but my bet is the compressor is ok. Greg

Reply to
Greg O

Does anything get brighter when you plug run the motor? I can see that the motor causes one circuit to get overloaded, which causes a second circuit to dim; but unless something gets brighter, your story does not make sense (at least not with a floating neutral)

Also, you say the 1/3hp motor causes the floodlight to dim, and the 1/2hp motor burns it out. That can't be. Or did I misread this?

Reply to
toller

He did try it on a different circuit and it ran OK. Yes, a 1/3 HP would only draw that much if it at a locked rotor. I wnet for the more common type problem, but in this case, it was a less obvious one.

Reply to
Edwin Pawlowski

Nothing got brighter, ALL lights got real dim, and the flood bulb was nearly off, just an orange glow.

I plugged the 1/2HP motor in a different circuit. That is when it blew.

However, I found the problem. I was looking in the breaker box when I plugged in the motor again, and I heard a pop sound. I decided to wiggle breakers and when I wiggled the main breaker the motor sped up and the lights got brighter for a second. That's when I shut off the power and pulled the main breaker. Sure enough, the contacts were spread apart too much on one side of the line. That breaker always looked crooked, and now it's straight. I think it was tipped and the contacts on one side of the line were off to the side of the panel pegs, instead of being clamped around them. I tightened them with a plyers, put the breaker back, turned on the power, and everything works again.

Therefore, it appears that one side of the line was not making good contact. This explains why my welder tended to shut off for a few seconds every once and a while, when I was running it on high. This started right after I replaced the old wiring and old fuse box.

What I dont understand is why my 220V submercible well pump still worked. It's on the same main breaker, (plus its own 20A dual breaker). It must have been running on 110V, but still worked fine. This makes no sense.

Now that everything is fixed, I have one question. How in the heck can the lights work at all on that side of the line, and what caused them to get dim when I plugged in a motor? Also, it would appear that the flood light got too much voltage, since it got real bright and blew the second I plugged in the 1/2HP motor?

Mark

Reply to
maradcliff

Perhaps at 220 volts the pump uses less current than the 120 volt motor driven items, thus less of a voltage drop. Even if the voltage drop was, say 50 volts, the 220 volt motor would still have a higher ratio of power left.

--Mike

Reply to
Mike Fritz

Check for loose connections especially on the neutral. Lights dimming under an load is an sign of an loose neutral. Well one of the signs there are other things that could be causing it.

Reply to
SQLit

this is Turtle.

The loose connection just came into play with what you said here. It can be a Loose neutral but it can be a loose hot too. Also you have contactor in the breaker that can be burning and causing the shot. They have contactor just like switches to turn it off and on.

Yes , I have seen a few problem with ITE breaker here lately.