1/2" Conduit for basement sub panel

Hello,

Our new house has a 1/2" conduit from the main panel to our unfinished basement. Yes, I requested a 3/4" minimum but the contractor knows much more than I do! :(

I want to run a sub panel using this conduit. The total distance may be about 100'. I plan on running at least 4 circuits off this panel ie. 20A for plugs, 15A for lights etc...

What size wire should I run in the 1/2" conduit for this subpanel?

Is there a special type of wire for this application (stranded vs. solid)

I would like to run #8 but not sure if it will fit. What configuration would be best. 120V only no dryers or any need for 240V.

Thanks.

Dan

Reply to
D
Loading thread data ...

Get a copy of "Wiring Simplified." Understand what you're proposing, and decide for yourself whether or not it's over your abilities.

There are bigger and more expensive books, but that one's a pretty good, "Do I feel up to this" kind of book, filled with lots of warnings about how not to kill yourself.

IF you still feel up to it, make sure that in Yakima, it's not required to have a liscensed electrician do the work.

You still with me? Okay. Head to the library reference room with a big notebook.

  1. Using a good electricians reference or electrical engineering handbook, calculate the size wire you need for 2% voltage drop on your
100' run.

  1. Check against the NEC. If what you calculate is smaller than their requirement, follow the NEC. They're the law, not you.

  2. Using the ampacity figure from step 1, look up in the NEC how big a grounding wire you need.

  1. Using the tables in the NEC, calculate the total area of your wire for all the conductors you specified in steps 1-3. Remember that you'll have THREE conductors to carry current, plus a (probably) smaller grounding conductor.

  2. ESPECIALLY if you've not pulled wire before, multiply that by 4. That gives you the minimum conduit area for 25% fill. Why? Feel free to use 40%, but I wouldn't want to do it.

  1. Find the cross sectional area of your intended type of conduit in the appropriate NEC table and find the smallest trade size that's larger than the number you've just calculated.

  2. Double and triple check all your calculations. Now do it again.

  1. If this seems too involved, hire a professional. Not to be flippant, but what you're proposing is nontrivial, and there are a lot of details you want to get right.

Reply to
Charles Krug

Is the conduit 100'? If there's nothing in it already you are going to have a hard time even getting 10 gauge in there and that probably won't be enough for what you need.

Reply to
Brad

Use THHN stranded. Although you are allowed 3 #8 in 1/2", as the other poster said it will be a really tough pull. Unless...you can insert one or more pull boxes along the way. If the inspector will require a separate equip grounding conductor, you'll be out of luck on fill capacity.

#10 stranded THHN sounds like a better way to go, giving you a 30 Amp subpanel, probably plenty (compute the loads).

Jim

Reply to
Speedy Jim

snipped-for-privacy@ci.yakima.wa.us (D) wrote in news: snipped-for-privacy@posting.google.com:

Did you specify the 3/4" in writing? If so, put it on the punch list to be fixed BEFORE he gets final payment on the construction. Especially if he charged extra for the 3/4" that he didn't install.

Matt

Reply to
TIA

Thanks for all the replies.

I had a licensed electrician come to take a look at the problem.

Currently, there is only about 60' of 1/2" metal conduit and from there to were I would place a sub panel is about 20 - 30' max. He has told me that code will not allow 3 #8 conductors in a 1/2" conduit and has suggested running a new conduit to supply the sub-panel. This would involve #6 wire for a 60A sub-panel. The total cost of about $400.

He mentioned that I could get 3-20A circuits or 4-15A circuits in the

1/2" conduit without adding a sub-panel. I may opt for the 3-20A approach since I am looking at plugs and lights mostly.

Is there any way to get 4-20A circuits in that 1/2" or even 2-20A and

2-15A?

Thanks.

Dan

Reply to
D

You need to make the contractor remove the 1/2" conduit and replace it with 3/4" conduit, at their expense. Their mistake, they pay. Hope you got it in writing!

Reply to