I'm going to purchase a air compressor which as a 7hp rating so I guess it's really a 5hp compressor. My shop has a 40amp 240v feed to my subpanel. Question, how many amp breaker is needed and typically what current does a compressor like this draw.
Regards
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Ask the Vendor about the AMP rating of the motor is the only REAL way to know
Frankly, if this is more than a real 3hp motor, I would be very surprised
John
On Wed, 18 Aug 2004 21:35:22 -0400, "Woodchuck"

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
You need to look at the plate on the motor to see how many amps it draws.

it's
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

it's
It may be less than you think! I have a 7 HP Porter Cable compressor, it is in reality about 3 HP. The specs you need to know will be on the motor. You need to size the breaker so the motor draw as lower than 80% of the breakers rating. In my case the motor was rated at 15 amps@ 240 volts, I am running it on a double pole 20 amp breaker. Greg
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

it's
You should be able to find the current specs from the vendor's web site. I would not be surprised to see it hovering around 20A.
--

-Mike-
snipped-for-privacy@sprintmail.com
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
"Woodchuck" writes:

it's
Use a 2P-40A branch c'bkr and #8 AWG, 2 conductor /w/ ground to feed the compressor.
It's what I've used for a 5HP, 2 stage unit for the last 10 years.
HTH
Lew
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
I have an Ingersol Rand 60 gal and it only draws 15 amps @ 240v. I was only going to run it off our secondary clothes dryer feed (we no longer use it). It would have been an easy hookup, but my electrician said that the 40A could possibly be too much for it. For the price of a new breaker I have a better piece of mind that I am not going to overload the motor with 40 A when it only requires 15A. So I gave it a 20A breaker/
Rich

a
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
"Searcher" writes:
only

it).
That is a common misunderstanding of the relationship between a c'bkr and a motor.
The c'bkr does NOT protect the motor, only the insulation on the wires feeding the motor.
There are conditions where a 20A c'bkr will nuisance trip on a 5 HP motor.
If you truly want to protect the motor, you must add an overload relay.
HTH
Lew
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Most motors in the consumer market have internal overload protection. The allowable overcurrent device is generally allowed to be up to 250% of the FLA on the nameplate, rounded UP to the next standard breaker size. Legally you could put a 15a FLA motor on 14 ga wire (you CAN use 310-16 not 240.4(D)) with a 40a breaker (430.52). At that point voltage drop would be a bigger consideration than anything else.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

If that's your electrician's understanding of electricity, you need a new electrician.
Kevin
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
If your electrician said that, fire him. Amperage draw is determined by the motor, not the breaker.

guess
does
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

the
Not necessarily so. His electrician may have meant that he should protect both his wiring and his motor with the proper breaker. Yes, the breaker primarily protects the wire, but it also protects the device at the end of the wire. A failure in the motor that won't trip the breaker until it draws 40A will be more catastrophic than one that will trip the breaker at 20A. His electrician is correct in stating that he should size the breaker to the load that will go on it.
--

-Mike-
snipped-for-privacy@sprintmail.com
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
The breaker is there to protect the wiring, and that's all. If you believe as you say, anytime you go to use an appliance, turn them all on as that circuit will be underloaded if you don't. Never use a single corded drill in your shop. Best turn on the dust collector too in order to load the circuit. How's your power bill? Things must work in strange ways around your house.

current
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I
feed
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

What he is talking about is the different facets of protection in a motor circuit. The branch circuit breaker is only there to protect from a short circuit. Overload protection is another part of the system and that is what protects the motor. It is also what keeps the wire from overheating. That is why you can have things like #14 wire on a 40a breaker and still be legal. See the diagram at the beginning of NEC 430 to get a better understanding.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thanks Greg. Saved me the trouble.

a
what
be
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Not actually. Greg responded with something intelligble while your response both ignored what I had originally posted and jumped way too fast at the chance to post a wise ass comment. Neither of those characteristics served to credit you.
So let me ask you a question - would you connect your 220V tablesaw directly to the main breaker in your panel? Besides the code requirement for a branch circuit, and wire size, why not? Isn't it because circuits are sized to the application?
--

-Mike-
snipped-for-privacy@sprintmail.com
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Maybe we should just tell people to follow the 240.4(D) rule (15a = 14ga, 20a = 12 ga, 30a -ga) and ignore the 430 rules altogether since they seem to be over everyone's head. It just isn't what the code allows.
430 "motor" rules do require the circuit to be sized to the motor served.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

directly
sized
20a
to be

Not at all Greg - I appreciate you mentioning the 430 rule - something I'm not familiar with and can stand to learn from. My reply was more in response to CW's condescending tone than it was related to anything factual about electricity.
--

-Mike-
snipped-for-privacy@sprintmail.com
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
You do seem to have a bit of a comprehension problem. Breakers are sized to protect the wiring. How many 350ma breakers do you have for electric clocks? You must have a whole bank of them for individual light. Do you have a separate building to house all these?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Site Timeline

Related Threads

    HomeOwnersHub.com is a website for homeowners and building and maintenance pros. It is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.