I recently inherited my dad's Delta/Rockwell Unisaw with a 220V motor. The saw is a dream to use compared to my old Craftsman.

Luckily my shop is wired for 220 but I have a wiring question...

The wall plug is a 4 blade and the saw has a 3 blade plug so I need a new plug for the saw. I was going to just buy a new 4 blade male plug and replace the existing 3 blade on the saw.

So do I wire the ground/common from the saw to the ground or to the common on the plug? I can't seem to figure out which is appropriate.

Or should I just buy a length of 12/3 and use all 4 lugs? Does it matter? I assume if I did that all I would need to do is screw the ground to the saw frame somewhere... right?

Reply to
LA
Loading thread data ...

No.

The saw needs two hots (of opposite phase) and a ground to function. It does not want or need neutral. The 4-prong plug will work fine. From the saw, connect hot, hot and ground to the appropriate prongs. Do not connect anything to the neutral prong. Its that simple.

Regards,

Steve

Reply to
Stephen M

If it's wired correctly, in your four plug wall receptacle there should be two hot leads, a ground, and a common (white) for a total of four. The latter (white) is used with one of the hot leads to supply 120v to appliance lights, timers, etc.

All you need to wire the saw correctly is the two hot leads and a ground.

If it were mine, I would change the wall plug to an appropriate female receptacle, wired as last above, for your saw's male plug, and cap off the common (white) with a wire nut and some electrician's tape, just in case you/next owner ever wants to plug a dryer/appliance back in.

Reply to
Swingman

Thanks Steve. That IS simple!

Reply to
LA

First, before you make any changes, check the rating of the wiring to your 240V receptacle and check the rating of the fuse or circuit breaker protecting the wiring. The rating of the circuit breaker and wiring determines the receptacle used. If the circuit is not rated for 20 Amperes or is rated for more than 20 Amperes, then you'll be best served by having an electrician do what is necessary to get you a 240V 20A circuit.

Note that running your saw on a 50A dryer or range circuit is very dangerous, as the saw internal wiring, cord wiring and motor are not able to handle the large overcurrents that the 50A circuit is capable of providing.

If the circuit is a 20A 240V circuit and the wiring is at least 12AWG, replace the wall receptacle with the correct NEMA fitting to match the plug on the saw.

What you have on the saw is either a NEMA 6-15P or 6-20P. What you have on the wall is probably a NEMA 14-30R (or 14-50R).

Replace the NEMA 14-[53]0R on the wall with a NEMA 6-20R (which will accomodate either a NEMA 6-15P or 6-20P plug). When you replace the receptacle, clip the stripped end of the grounded (neutral/white) conductor, tape it off and stuff it back in the box; the NEMA 6-20R receptacle needs only the two current carrying conductors(typ. black & red) and the grounding (bare/green) conductor.

There is no point in running the grounded (aka neutral) conductor from the receptacle to the saw.

For NEMA patterns:

scott

Reply to
Scott Lurndal

This statement makes no sense to me. I can run my 3.5A drill just fine on a

15A 120V circuit. I can run a 100W light (0.8A?) just fine on the same 120V circuit. Heck, I can run a 6W (0.05A) light off a 120V 20A circuit, if I like. None of these are considered dangerous.

I'm not an electrician and I don't play one on TV, but my understanding is that the circuit breakers are designed to protect the circuit and plug, not the devices plugged into them. The motors typically have a thermal overload protector that switches them off if they over-heat or draw too much power. If the manufacturer is really concerned about that, they can provide a fuse on the device to protect it.

Clint

Reply to
Clint

Not to put too fine a point on it, but your saw only *needs* the two hots to run. True, there *ought* to be a ground, too, but that's a safety issue (and a pretty significant one), not a requirement for the motor to run.

If it were me, I'd get a length of 12 ga SJ cord (it has black, white, and green wires--all you need) at the big box and make myself an extension cord. Get an inline receptacle to match the plug on your saw and put it on one end of the cord, wired hot-hot-ground, and get an inline plug to match the receptacle on your wall and wire it hot-hot-ground. Ignore the neutral connection on the plug.

The nice thing about the SJ is it's usually bright yellow, so as to not readily disappear when/if underfoot.

Finally, what kind of plug is on the saw? If it's a molded (to the cord) plug, with a (--.--) configuration (which is a 240V 15 A Nema style), I'd leave it on. I consider the molded 240V cordsets to be like gold, but that's only in terms of trying to replace one.

Lots of people like the twist locks (I have one on my feed from the ceiling, but it's the first one I've had in 30 years), but they are bulkier and more expensive than the equivalent to your plug.

If there's a different plug on the cord, either put whatever you want on it or just select a matching receptacle when making up the extension cord.

Reply to
LRod

I've found it's usually cheaper (and easier) to just get an extension cord with the right ends to match one side, and cut off the other end. That leaves just one plug end to buy and wire up. Less work and less money than building your own from scratch.

Reply to
Roy Smith

Thanks all... I think you straightened me out and I know what to do next.

I appreciate the help!

Reply to
LA

Great idea for 120V. Where do you find 240V extension cords?

Reply to
LRod

Circuit breakers are designed to protect, first and foremost, the wiring from the circuit breaker to the protected device. The code makes exceptions for 20A circuits, as UL-listed small-appliance wiring is rated sufficiently to handle the transient overcurrent conditions on 20A circuits.

However, once the circuit breaker is rated higher than 20A, the code requires that everything downstream of the breaker (wiring, switches and motors) to be rated for minimum current matching the breaker.

Feeding 50A through #12AWG wiring is a recipe for disaster. Just because your saw doesn't pull 50A normally, doesn't mean that it won't pull that during a blade stall, for example. Melted wiring smells bad and causes other inconvenient events, like fires.

While the motor _may_ have thermal overload protection, and if you have an industrial motor controller, it also has thermal protection, the O.P. was planning on plugging his saw into the recept. That means #12 awg in the path between the overcurrent protection device (the circuit breaker) and the motor/motor-controller. That's your weak spot, and one of the areas the code is intending to protect.

Please read and understand the code. The manufacturer has no control over the wiring between the circuit breaker and his device.

scott

Reply to
Scott Lurndal

There are several Ace Hardwares in my city that would have these. I usually buy extension cords for wire stock and buy any plugs needed for special applications.

Bob AZ

Reply to
Bob AZ

Home Depot lists some (in the guise of 6' appliance pigtails) on their web site. Other than that, I'd try a welding supply place or an appliance store (especially one that sells lots of big air conditioners).

Google for "extension cord 6-20" and you'll find a few sources. Granted, they're pretty rare compared to standard 120V cords.

Reply to
Roy Smith

You don't care, all you want is the wire.

Buy the lowest cost, #10, 2Wire with ground, molded cord set you can find.

Whack of the female and wire that end to the saw.

If the male plug is not what you want, whack it off and wire the correct one on to that end.

For a table saw, I like a 30A, locking plug, but that is my preference.

Problem solved, you'll be money ahead.

Lew

Reply to
Lew Hodgett

I make mine. It's just a wire with a plug on one end, and a socket on the other. Any electrical supply house can get you all the parts you need (all three of them ;).

Reply to
DJ Delorie

Huh? Keep reading.

Okay, I get that part, although finding the #10 might be a chore...

This is my point. NEITHER of the ends will be what you want if the cord isn't a 240V extension cord. And to those who pointed out the 6' A/C extension cords, your saw must sit a lot closer to the wall with the socket than mine does. I figured 10-15' every time I've done it.

Well, the "money ahead" may amount to as much as $5-10, and none at all if you use the locking sets, which makes my SJ roll-your-own look just as attractive.

But, producing feline leather can be done a number of different ways.

Reply to
LRod

That's called shopping.

Home Desparate should have them.

Sure they will. One end is hard wired to the saw, the other to a plug req'd.

BTW, the minimum insulation for cordage like SJ is 300V.

I'm with you which is why I suggested a 25 ft extension cord in the first place.

A molded cordset is the lowest cost way to get a piece of cable.

You don't have to buy Hubbel. Lots of people make locking devices.

I like my Model 12 Winchester for felines.

Lew

Reply to
Lew Hodgett

I'm impressed by the quoting of plug and socket types in your your post, but the last sentence of the first paragraph, and the whole second paragraph quoted above are just SO WRONG!

Reply to
lwasserm

NEC stops at the socket for devices that plug in. Put a plug to match the exisiting socket on your saw and you'll be fine.

Reply to
lwasserm

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.