Wiring out to a consumer box?

Need your help guys.

I'm installing a consumer box to a workshop/garage extension on a small shop to provide power for 4 fluorescent tubes lights and 6 double gang power sockets. Power sockets will only be used for drills, one shutter roller motor and hand lights and such like but not any heavy bench stuff.

My local electrical retailer has supplied me with a 4 way CU with 32A and 6A MCBs for sockets and lighting. He has suggested to me that I need to run a 6mm T&E cable from the original CU and wire into a 40A MCB there.

I have conflicting info from an electrician friend of a friend who says I should run the meter tails at the original CU to a 100A junction box and then run 16mm cables to the Garage CU and original CU. This seems like overkill to me.

Who is right here?

The garage CU is 12 metres from the original CU and the garage is connected directly to the main building.

Cheers

Reply to
StealthUK
Loading thread data ...

IMHO the retailer. The cable to the new CU needs to protected somehow. With your friend's suggestion it wouldn't be... Also 16mm is as you say, way overkill... Is he really an electrican or just pretending to be one??

Reply to
BillR

This is one way of doing it. However, it would suffer from lack of discrimination. This means that a fault on the socket circuits is as likely to blow the 40A MCB as the 32A one. This would knock out the lights at, perhaps, a critical moment. (Large dangerous power tools still spinning down). You might get slightly better discrimination fitting a Type C 40A MCB to the master consumer unit, although it won't be guaranteed at all. The MCB there is only protecting the submain to the garage, not the equipment connected therein.

This is a "better" solution, but might not be required depending on your attitude to the lack of discrimination and the ease and expense of running such large cables. You should consider this if there is the slightest possibility that the garage might require a beefier supply in the future.

Also, I would strongly recommend using an 32A RCBO instead of an MCB for the socket circuits. Power tools are crying out to be so protected.

Christian.

Reply to
Christian McArdle

P.S. I forgot to mention that the 16mm tails would have to be protected by a suitably rated switchfuse after the Henley block. You can only count on the electricity company allowing about 2m of cable to be protected by their service fuse.

Christian.

Reply to
Christian McArdle

"StealthUK" wrote | I'm installing a consumer box to a workshop/garage extension | on a small shop to provide power for 4 fluorescent tubes lights | and 6 double gang power sockets. Power sockets will only be used | for drills, one shutter roller motor and hand lights and such | like but not any heavy bench stuff. | My local electrical retailer has supplied me with a 4 way CU with | 32A and 6A MCBs for sockets and lighting.

One of each? Total load = 32+6 = 40A. What about RCD protection for the sockets, though?

| He has suggested to me that I need to run a 6mm T&E cable from the | original CU and wire into a 40A MCB there.

That sounds sensible. (However the existing load on the consumer unit and its supply must be considered.) It is possible 10mm might be required, though, and might be wise to install now to allow for future increase in load anyway. You may also need to run a parallel 10mm earth wire to the secondary CU, as the circuit protective conductor in the 10mm cable may not be adequate. This must be ascertained by calculation or test.

The secondary CU should normally be supplied from a non-RCD circuit on the main CU.

| I have conflicting info from an electrician friend of a friend who | says I should run the meter tails at the original CU to a 100A | junction box and then run 16mm cables to the Garage CU and original | CU. This seems like overkill to me.

You cannot run unfused 16mm meter tails 12 metres. A switchfuse would be required, and the meter tails into the switchfuse should be 25mm anyway these days.

As this is business premises, the Electricity at Work Regulations 1989 SI

1989 No 635 will apply, and you may wish to acquaint yourself with the Memorandum of Guidance HSE SH(R)25. It is reasonably safe to assume that current IEE Wiring Regulations and appropriate British Standards have 'deemed to satisfy' status for compliance with the EAW Regs. The installation will therefore have to have a full Design schedule signed off by a competent person, along with the Installation itself, and the pre-energisation inspection and live testing carried out, with full compliance with the design requirements verified, before the full completion certificate can be given. In the event of an accident or fatality, anything less would probably not be acceptable as a defence in Court.

Owain

Reply to
Owain

If its not commercial, also consider a non RCD supply for a freezer out in the garage.

Mungo

Reply to
Mungo Henning

Thanks for the advice guys. I am placing a RCBO in as well now. I want to do this job properly so am taking my time. The consumer box and ring circuit, lighting etc have all been done. I'm now working on electrical stuff in the shop itself. The state of the wiring is a real mess and the last supposed electrician who was supposed to have cleaned up the wiring and added new lighting did a really bad job. He had run 1.0 mm cable direct from the mcbs and just left it hanging over the consumer box itself (no clipping etc). He also left his business sticker on the consumer box, maybe I should give him a call! Someone also decided to leave a live junction box without its lid amongst a whole mess of cables which was a real nice touch. I've now replaced the 1.0mm with 1.5mm and clipped it up properly.

Regards the guy who gave advice about running 16mm tails from a 100A junction box, he works for a council doing electrical work in council houses etc.