Wiring an electrical shower

Looking to buy and install an electrical shower.

I already have a 6m^2 cable running from the CU to the shower. The length of the cable is only 2m, and at present it is connected to its own 40A MCB.

Would this cable be ok for a 9.5kW shower, or would it only be sufficient for an 8.5kW? According to Mira's manual it appears to be ok (see

formatting link
the last paragraph on p15).

Also, I am finding it difficult to get hold of a 45A MCB, would a 50A be ok?

TIA.

Reply to
NotMe
Loading thread data ...

At that length 6mm sq will be fine (voltage drop is only 0.6V)

Given the nominal load is only 39.58A at 240V I would stick with the current MCB.

Reply to
John Rumm

..except shouldn't the rating be at nominally 230v these days, i.e. 41.3A, or are showers rated at the highest mains value rathter than nominal ?

Reply to
Mike Harrison

showers rated at

The nominal rating of the shower will be 230V +10%/-6% although the actual voltage that it will be run on will obviously be 240V in reality.

If you do the sums for 230V then you are still in budget on the cable (assuming it is clipped direct and not in insulation or buried etc) and get a current rating of 41.3A. A 40A MCB will supply that indefinitely. It would also be worth doing a check on the earth loop impedance to make sure you get the required disconnect time etc.

If the cable is in insulation or subject to other derrating factors then an upgrade ought to be in order (or a smaller shower).

Reply to
John Rumm

41.3A, or are showers rated at

Thanks for that - I reached the same figure with my calculations.

The cable run is a follows: 1.5m in a very large cavity (clipped in a space above a false ceiling, some 1m from the original one), and the last 0.5m in a lath and plaster wall with no insulation.

By reckoning it should be ok with 9.5kW. What do you think?

Thanks again.

Reply to
NotMe

or are showers rated at

There's usually two ratings. The load is largely ohms law resistive. It will normally be quoted at 240V and 230V. You should plan for the 240V rating. The 230V rating will actually draw less current, so you'll undersize the protection. Normally to 240V rating is the headline figure. On 230V, a 9.5kW shower will be an 8.7kW shower and draw about 38A.

Remember, it won't trip at 40.00001A anyway. There's LOADS of leeway. As long as it is nominally below the rating by calculation, it doesn't matter if factors (i.e. supply overvoltage, element overrating) leads to an amp or two over).

Christian.

Reply to
Christian McArdle

or even 10 or 20!

Reply to
John Rumm

From a current point of view that sounds fine. Same goes for the MCB.

(If you were planning on a larger shower (i.e. 10.5kW or bigger) then replacing the cable would probably be required)

Is the shower going on a RCD protected feed?

Reply to
John Rumm

Well, but you shouldn't plan for it to above the nominal rating. If the actual turned out to be 10 or 20A over, then your planning was a little deficient, maybe?

Christian.

Reply to
Christian McArdle

Yep, 82204 on

formatting link

Reply to
NotMe

I should point out that I was not suggesting that you design with that sort of overload in mind, I was more highlighting that, contrary to popular belief, a 40A MCB will happily supply a 25% or 50% overload for a significant time without tripping.

Reply to
John Rumm

That saves needing to get into too much detail on earth fault loop impedances and disconnect times then ;-)