Thanks for the earlier advice on subject "Chaffoteaux FlexiFlame 140 boiler periodically cutting out". The decision has now been made to replace it, and the recommendation we have, which I think is reasonable, is to replace the ancient 41kW beastie with a pair of 24kW Worcester-Bosch system boilers (model 24i) running in parallel.
This existing system is sealed, and the Chaffoteaux has an internal pump circulating primary water through a low-loss header* (LLH), and there is a separate pump circulating the LLH contents around the radiators which are spread over 4 floors, see ASCII art below. This is heating only, no domestic hot water.
Currently one radiator is open valved and the others have TRVs.
The proposal is that the two new boilers will each have their own pump and check valve, and that combination will be connected in parallel and tee'd into the existing low-loss header. A magnetic strainer will be included.
So far that seems straightforward. My concern is the control system to ensure the pair of boilers work at maximum efficiency. When it is mild we want one boiler only to be running, and the second cutting in only when more that 24kW is required. Clearly one boiler running at full power will be much more efficient than two running at half power. and for most of the year we should see the benefit of full condensing operation of one boiler with the other hardly ever firing.
First question is, is there a standard 'box of tricks' that does this? I have asked W-B who insist they "don't do system design just make boilers" and could offer no help.
It shouldn't be too difficult to make a controller to do this... my early thoughts are that starting from a cold system, I want to stop #2 boiler from firing for say 1/2 hour to establish if #1 is coping or not. That can be decided by checking the temperature rise across the boiler; once its stabilized (after the 1/2 hr) I can say that if it is greater that the spec figure of (say) 11 degrees then it is dumping its full
24kW into the system and #2 needs to be turned on to supplement it.So far so good, but with two boilers now running, how do I control things so that #1 stays at full power and #2 modulates as required until conditions require #2 to be turned off entirely and then #1 modulates down. I can see there is scope for instability and hunting here if I'm not careful.
I'm sure this has all been done before but not sure where to start looking, having no experience of industrial systems.
Any clues please?
*Chaffoteaux refer to the LLH as a "monotube", which appears to be simply a 600mm length of 54mm tube with the boiler flow and return teed in near each end, and the radiator system connected at each end with 28/54mm reducers as below. [Fixed font ASCII art]To Boiler || || (P) || __||________||__ ====________________==== || 54mm || || || 28mm || (P ) || || To Radiators