Is it a definite no no to plug said heater into a switched 13A socket high on the wall? TIA
- posted
15 years ago
Is it a definite no no to plug said heater into a switched 13A socket high on the wall? TIA
Always used to be, but under new regulations you might be lucky if your bathroom is big enough.
Someone will be a long in a minute :-)
Pete
The only alternative I can see is to hardwire it into a pull-switch.
Yep - there are higher-power pull-switches for just such purpose; my parents used to have one until recently. However, as I said, sockets are now allowed in bathrooms provided they're far enough away from baths, sinks, etc. This distance is expressed as "zones" and the different fittings that are allowed in them. I don't have all the details to hand, but I bet if you Google _bathroom zones_ or something similar you'd find them.
Pete
Cheers Pete
Pete Verdon coughed up some electrons that declared:
Sockets are only permitted over 3m from Zone 1.
Other than shaver sockets.
But the rules on "current using appliances" that are hard wired in are different. I think it can come off a fused spur as long as it's >0.6m from the edge of Zone 1 (bath or shower edge), ie it's outside of the zones.
Sockets are a special case due to morons and hairdryers.
Brass Monkey:
How far away from the bath/shower edge can you get the heater - and how high? If you can tell us, I'll look it up and quote verbatim.
Would the heater be one designed for bathroom use?
Cheers
Tim
Tim, this is the heater -
Brass Monkey coughed up some electrons that declared:
That's sockets out then unless you want to wire it to the German regs (VDE100) then apparently you can have a shuko...
Bath = 0.7m typically, so the rest of the rest of the room is about 1m ish
OK, that sounds like it will be within Zone 2 (0.6m from bath edge)
2.25m above floor is outside of the zones, even over the bath.This is one of the more sane ones...
OK - If you are within 0.6m of the edge of the bath, you need a device rated to at least IPx4, which is going to be fundamentally hard with a fan heater.
The B&Q one you mention is certainly not suitable.
Can you get the heater clear of Zone 2 (> 0.6 m from bath edge) by pushing it into the far corner or on the other wall? If so, use any hard wired heater, though pull cord controls would be preferable.
Or - if above the door is higher than 2.25m to the base of the fan heater, according to the regs I think you can have it - you'd need a very slim heater or higher than average ceilings.
Cheers
Tim
Thanks muchly, Tim. It's in the corner on a pull-switch.
Do what anyone else would.. wire it to a fused spare outside the room. Its earthed and you don't need to touch it so it is as safe as it can be. You can add and rcd but it does practically nothing to make it safer.
dennis@home coughed up some electrons that declared:
This is correct, but the appliance still needs to meet IPx4 to be in Zone 2, no matter where the supply is.
one of these in zone 3
HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.