storage heater in bathroom

Family friend has had an old storage heater in bathroom.It packed up so a firm has fitted them a new one. It is rated for use in bathrooms but is exactly half the size needed to heat the room and they way overcharged for the privedge. It does have no control switches unlike the correct sized heater.the heater is about 85cms from fixed bath...and is on economy 7,but only prtected by a wired wylex fuse.Also in the bathroom is one of those olde worlde ring radiant heaters and that IS within 60cms of the bath,with a low ceiling height to boot.would the corrected sized heater protected by a rcd spur ,and remove the light,for a splashproof bulkhead be an OK answer? I am going to sound out my pet electrian tomorow,part P and wll that.thanks in advance

Reply to
richard
Loading thread data ...

Aren't they always exactly half the size needed to heat the room, regardless how big they are? ;-) In this country at least.

Dad had a flat in Paris, and that had one giant storage heater in the central hallway, which was big enough to heat the whole flat for over a day on a full charge, and so worked well. The ones fitted in this country never seem to though - always much too small.

It sounds like a room which was probably wired to the

14th Ed regs (without actually digging out my 14th Ed regs). Replacing the storage heater like-for-like providing things like the equipotential bonding are all in place is still OK today.

If you want to bring it up to 17th Edition regs, you really need to do the whole room, and that's going to be more than one circuit. The regs are not designed with a view of mixing different editions in the same circuits, or same bathroom. Even in the overlap periods between editions, you must use entirely one or the other.

Reply to
Andrew Gabriel

If the heater is intended for a bathroom it can have no touchable switches. If there is another heater, it will be fine for background heat and will only fall short in very cold weather.

Reply to
harry

What heater you can fit comes down to the zones.

In a small bathroom you are probably limited to a TSR9AW (single element) s= torage heater, if insufficient fit a pullcord operated fan wall heater with= perhaps runback timer set to 5-10-15mins etc (FX20VL).

In a large bathroom, such as ensuite conversion of a very large room, it ma= y be possible to locate the heater and controls far outside the zones so an= y may be fitted.

Very true re undersized heaters.

- Conventional storage heaters require 2006 levels of insulation

- Conventional storage heaters do not work well, however, with 2012 levels = of insulation because the room stays too hot - door must be left open 24/7.= In this instance you need fan storage heaters such as Elnur 2kW 3kW 4kW AD= L-4012 etc which use a fan to pull heat out on call from a separate wall mo= unted thermostat. Unfortunately the addition of more insulation & fan pushe= s the price even higher. An alternative is to deliberately use an undersize= d conventional storage heater - with on-demand peak heating on a decent the= rmostat. Dimplex Duoheat combine both, but I am wary of their reliability r= e PCBs, thin film element and so on.

Bathrooms cry out for wall mounted IPx4 fan heaters unless well insulated :=

-)

Reply to
js.b1

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.