2m and 3m come up quite often as the limit before a switch fuse is required IME.
I can see the need for a fuse to offer fault protection, since a fault on the submain may otherwise not be cleared in time, and would result in taking out a fuse on the distributors side of the network.
The need for a RCD could only be driven by two possibilities, one being risk of direct contact, and the second being a loop impedance that is too high to reliably clear a fault. The chances of the former on a SWA submain are to all intents and purposes nil, and the later we know not to be true in this case.
(Don't think I have actually met a TN-S system yet that was as bad as the "notional" value).
A fuse is also probably better here in that it will discriminate with just about any MCB you care to use.
That is probably quite likely. They won't always be able to offer TN-S with a very low impedance.
Quick bung from one of the MCB manufacturers perhaps ;-)
Not really - I like to have all potential questions answered as well ;-)
One presumes the distance to the shed lights remains the same either way, so house circuit fed shed lighting is unlikely to dim less than a submain based installation (more in all probability!). This sounds like an example of complying with the letter rather than the spirit of the rule ;-)
I usually have a policy of making sure that anything outside does not share a RCD with something inside. Since the outside circuits are a more likely source of nuisance trips etc.
Here I have installed two split load CUs in the house[1] (preceded by one main switch in a separate two module enclosure)). Both TT, the second smaller CU is reserved for outside stuff. The 30mA RCD carries outside sockets and lights, the 100mA type S RCD directly feeding things like the garage and my workshop (via BS 88 cartridge fuse carries). The garage/workshop has another split load CU with inside lights on the main switch part, and sockets and outside lights on the
30mA RCD section. [1] When we got here there was one CU with everything sharing a single 30mA trip RCD. Needless to say a horse farting would plunge the place into darkness.
That's ok then!