Actually, when you get down to technicalities remember:
Electrician registered with Part P scheme...
- Works do not have to comply with BS7671
- Works merely have to be "safe" in their view
Engineer who wrote BS7671, DIYer or non Part-P elec...
- Works must comply with BS7671 (incl competency, right materials etc)
- Works should comply with AD "P" w.r.t. Notifiable or Non-Notifiable
If unhappy with a Part P registered spark take it up with the scheme provider. Could be the electrician used is a 5-day DI.
You would only take an electrician to court if...
- They installed 6mm CSA wiring through insulation and a 10.5kW shower
- ie, the installation is unlikely to be fit for purpose
You would not take an electrician to court if...
- They installed a LONG run of 10mm CSA wiring to a 10.5kW shower AND voltage drop exceeded that permitted
- ie, the electrician will argue shower's operation whilst slightly diminished will still function "reasonably"
To the OP, the problem with silicone/grout is corrosion of the terminals which in turn will create heating - damaging both the shower and the wiring to the shower. Something to remember when installing showers is where at all possible to conduit/trunking the cable in place (min 25mm) to avoid hacking tiles apart. Not always easy in tight bathrooms, but a lot better than "cable ends too short/ knackered", job becomes "rip apart the shower enclosure, tiles".