My Dad currently has an en-suite bathroom powered by a macerator. However he wishes to convert this to a normal flush only, but is concerned about the required fall for the waste pipe. Does anybody know what the required angle of elevation is for the waste pipe of a flush toilet?
thanks to anyone who takes the trouble to respond.
A good rule of thumb Paul, is a 10 mm drop for every 1 mtr of pipe length. Remember also that bends will have to follow this same requirement, so if the bend popping through the wall is part of a 1 mtr measurement, then it needs to follow the rule of 10 mm drop per 1 mtr of length.
"A minimum size 100mm branch pipe may be used for a maximum of 8 WC's or a length not exceeding 15m, gradient should be between 9mm and 90mm per meter run" Building regs 2000 edition.
From building regs. So min fall is 1:100 roughly.
Since this is a macerator replacement, he will want to work as near flat as possible.
The steeper gradients you quote are for washbasins and urinals and baths on smaller diameter pipes.
External falls depend on anticipated flow rate - i.e. number of bogs connected, and may be in large diamter pipe as low as 1:180. though
1:40- 1:80 is optimum. 1:60 is a good working figure.
From the chaotic regions of the Cryptosphere, The Natural Philosopher wrote on Fri, 01 Aug 2003 09:36:23 +0100:
The Building Regulations don't give guidance, the Approved Documents do. (2-0) Perhaps you should download the 2002 edition of AD 'H' (Drainage). (3-0)
Table 2 Common branch discharge pipes (unventilated) gives the gradient limits as:
Appliance |Max no. to |Gradient limits |be connected|mm fall per metre) ____________________________________________________ WC outlet > 80mm |8 |18(2) to 90 WC outlet < 80mm |1 |18 to 90
The footnote (2) to this table reads "May be reduced to 9mm on long drain runs where space is restricted, but only if more than 1 WC is connected". So for the OP's question relating to a single WC, then the minimum fall is 1:55 (4-0)
Very roughly. (Poor defending nearly let another in)
The lower end of the gradient range is uniform at 18mm/metre(1) across the whole range of appliances. (5-0)
The OP was about sanitary (above-ground) drainage. It sounds like you're getting this confused with the drains below ground. I don't know of any unpumped drainage serving normal domestic foul drainage that can be installed at 1:180! (6-0)
(1) In the UK we use the "metre" spelling for the measure of distance.
HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here.
All logos and trade names are the property of their respective owners.