Re: Cooker hood wiring



Neither is there for most lights. It presumably has its own on off switch?

Is it possible to wire it such that the cable comes out of the wall into it - ie behind it? If the cable comes out the top say near the back it's often the tidiest way to use an FCU or at least cord outlet even when wired off the lighting circuit.

Not a good idea, IMHO.

Can't see why you'd need one.

--
*A bartender is just a pharmacist with a limited inventory.

Dave Plowman snipped-for-privacy@argonet.co.uk London SW 12
  Click to see the full signature.
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

...but you need a means of isolating appliances containing motors.
You could use an FCU or an unfused double pole switch, or a bathroom fan isolating switch (ignoring the 3rd pole, but it will have an appropriate legend on it). Some cooker hoods have quite high power fans nowadays, so check the loading on your lighting circuit first.

You need to be able to operate it for maintenance of the cooker hood, i.e. before you open or take the hood down. It doesn't need to be accessible for normal day-to-day use. If it's far enough away (or out of sight) of the cooker hood such that someone working on the hood could not be said to be in direct control of it, it needs to be a type of switch which can be locked off. Bathroom fan isolating switches are often of this type, although they don't come with the lock (it engages in two tiny holes either side of the rocker, which you probably haven't noticed unless you looked for them, holding it in the off position).
BTW, and plug and socket is also acceptable means of isolation.

My cooker circuit has been turned into a switched radial circuit by fitting 3 socket outlets in place of the original hardwired cooker outlet. One has the oven plugged in, another has the gas hob ignition plugged in and the third was for some appliance previous occupant must have had in the cupboard under the oven. If your oven plugs into a 13A socket and you don't have electric hob, I see nothing wrong in doing this.
--
Andrew Gabriel

Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Provided the MCB/fuse is of a sensible rating, of course. (i.e. a 32A or 20A B curve). This will usually be the case, although frequently cooker circuits are wired with higher ratings, such as 40A or 45A, which would need swapping out. Also, you'll need to prove that the sockets aren't likely to be used for outdoor portable equipment, as they would need an RCD/RCBO.
Christian.
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

It is in this case, and 6mm² cable.

Well, there aren't any RCD's in this house at the moment. If I get round to it before Part P comes into force, I will fit a nice new CU with separate RCD protection on each ring, and take the immersion heater off the ring circuit. If I don't get round to it in time, it will stay with no RCD protection and with the immersion heater on the ring circuit forever more, or until it causes a fire and burns the house down...
--
Andrew Gabriel

Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Hi Andrew,
Thanks for your reply. I have decided to do the following:
Install a 13A socket behind the cooker hood which will be completely hidden. The cooker hood will be plugged into this. The socket will be connected to a visible FCU at worktop level. The FCU being on the kitchen ring circuit.
Does this sound as if it is in line with the regulations?
Thanks,
John
wrote:

think
switch?
an
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Yes, but you don't need the FCU. If the plug can't be withdrawn without first dismantling or removing the extractor fan, then a double pole 20A switch will do (unfused as there is a fuse in the 13A plug). If you can get to the plug for such maintenance, then you don't even need the switch. You don't need to be able to get to the plug or switch easily for everyday use -- they are isolating switches for maintenance, and not required for functional switching (hood presumably has its own switches built-in for that).
--
Andrew Gabriel

Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thanks Andrew, all a lot clearer now.
writes:

hidden.
to a

Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

<snipped>
You won't need any FCU in the circuit if you're making the socket in as part of the ring main. If you're making the socket for the cooker hood a spur off from the ring main in the kitchen, then a fused spur unit can be placed beside the socket where you're taking the spur from. Then you take a single cable up to the socket behind the cooker hood.
As long as the cooker hood can be completely isolated from the electric's, both live and neutral, for maintenance reasons, then that is all that is needed. This is why Andrew recommended either a double pole switch which breaks both live and neutral supply, or a switched fused spur if you were removing the plug.
A switched fused spur with flex outlet would be the neatest way, as this means you're only taking one cable from the existing ring circuit, and connecting the flex in to the switched fused spur, which is quite within the regulations.
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Yes, switching the spur (and not breaking the ring;-) You have to have a fuse somewhere, be it in a FCU or in the appliance plugtop, but you don't need more than one, and it doesn't have to be at the beginning of the spur.
--
Andrew Gabriel

Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Hi Andrew Gabriel In you wrote:

Stupid question alert....
What's an FCU? (Acronyms escape me sometimes....)
--
Fishter
unhook to email me | http://www.fishter.org.uk /
  Click to see the full signature.
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Fused Connection Unit.
And if that hasn't jogged your memory, it is a device the size of a single socket outlet that combines some or all of the following features.
1. A switch (optional) 2. An indicator light (optional) 3. A fuse (compulsory) 4. A flex outlet on the front (optional).
Christian.
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 28 Jul 2003 20:17:28 +0100, "John Greenwood"

I think I might be a little concerned about the environment that would exist behind the cooker hood. By virtue of the fact it is a cooker hood one expects the general area to get a bit warm, and maybe laced with condensation/steam and other environmentally unfriendly options.
That probably doesn't make it a problem for the regs as such, but page 2 of Electrical Commonsense #101 might apply.
The other issue I would raise in this situation is that if you needed to take the power off that cooker hood fast, do you intend that the cooker hood has to be stripped before the mains to it can be disconnected? If so, that doesn't sound like an ideal situation. It'll be a right royal pain in the butt if the fuse to the cooker hood blows and you've got to take the whole thing apart to check it out!
Andrew
Do you need a handyman service? Check out our web site at http://www.handymac.co.uk
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Tue, 29 Jul 2003 09:22:48 +0100, "John Greenwood"

Maybe a couple of ideas:
1) Take the cable thru one of the cupboards at the side of the cooker hood, and have the socket in there (you do have a side cupboard to the cooker hood?).
2) Channel down to beneath the work surface, and put the connection in a cupboard under there.
3) Take the connection up and to the side, wired into a fused spur.
Andrew