Power to an outbuilding

I am in danger of becoming the latest victim of "a little knowledge is a dangerous thing". I want to operate a 3-phase lathe and lighting in a new outbuilding and am trying to sort out what I need to do in the face of apparently conflicting advice. I suspect I do not have enough electrical theory to understand what I am being told.

Basically, the outbuilding is 25m from the house mains supply point. I think I need to run 3 core, 4sqmm armoured cable in a 450mm deep trench with a warning strip buried at 150mm. So far so good.(I intend to use 4mm as the extra expense over 2.5mm in negligible). The 3hp lathe is to be driven by a 3kw inverter, the documentation for which says it needs a 35A fuse. I tried to work this through on (IMO excellent)K Zone at

formatting link
and a 35A fuse is OK for the circuit. The Regs, however require an RCD in the outbuilding. If I try the calculation in K Zone again usine a 35A RCD, it tells me "NO", as the RCD is above the "corrected nominal current". Same result with 16A RCD etc. So which RCD / fuse do I have to use? Any advice respected. I intend to dig the trench myself but have a contractor carry out the electrical work, I just want to understand. Thanks, Charles Adams

Reply to
charles adams
Loading thread data ...

Remember that fuse/MCB ratings and RCD ratings are for different things - the fuse/MCB rating is the max continuous current before tripping. The RCD current rating (carrying capacity, not trip current) is the maximum it will break without damage, so on a circuit with a 35A fuse/MCB, you would expect to uprate the RCD to maybe 50 or 63A to ensure that a fault current that trips the overcurrent protection will not damage the RCD (e.g. weld the contacts together), compromising future leakage protection.

Reply to
Mike Harrison

Can I assume the inverter is in the outbuilding and you have a single phase supply to it?

35A is an unusual rating. I suspect a C32A MCB would provide suitable protection, although check with the manufacturer. As it will be pretty efficient, its normal current draw (not peak) will be less than 3kW, so there's plenty of diversity to get lights and sockets running too. However, you could bump up the connection to 40A if you're worried.

For a single phase 32A connection over 25m, I make it 4mm minimum. For 40A,

6mm minimum. At the outbuilding, you'll want a consumer unit with RCD, and MCBs.

I'd go for B/C32A for the inverter, B6A for lighting and B20A for some sockets. The inverter will only pull more than a few amps or so when the lathe is spinning up, so there is more headroom than you'd think at first. Also, you need to check what the inverter really wants in the way of protection. If they really do insist on fuses, you may need to choose a consumer unit that will accept HRC fuse carriers and do it the way they say. Wylex (and probably others) do DIN rail 35A HRC fuse carriers.

As this is intended for reasonably heavy use, you should use a split load consumer unit. You replace the switch incomer with a time delay 100mA RCD (63A/80A). The lighting goes off the "unprotected" side. Then you have a fast 30mA RCD (63A/80A) for the socket circuit and the inverter.

The consumer unit side should all be single phase. Only the connection between the inverter and the lathe should be 3 phase. However, the lathe might require additional protection, in the form of a triple pole MCB (i.e.

6A) mounted in a separate enclosure. Read the lathe instructions and inverter instructions to determine if additional protection is required.

You are obviously intending to install TT earthing. Make sure you measure the resistance using a proper tester, not a multimeter! It must be below 200 ohms.

Christian.

Reply to
Christian McArdle

Spot on.

This is one of the main reasons why I am puzzled. The draw for 3hp 1ph is 10A so whree does the 35A come from (speaking from cable rating point of view)? Would you advise 6sq.mm?

They do say "fuse 35A and and I imagine this is related to speed of intervention. But am I right?

Thankyou. I think i'm getting it!

The lathe is a 30 year old British beauty. However, instructions are sketchy at bet. The inverter is a Simantec G110 3kW and the instructions are so comprehensive I do not know where to start!

Again, I and my succeeding generations thank you.

Many thanks for this commonsense advice, Charles

Reply to
charles adams

Inverter manufacturers often are very specific about the required protection (speed of intervention may well be an issue). Siemens may well recommend the exact protection required, including a part number for the Siemens component (I assume you mean 'Sinamics' G110?) - the drives we use certainly do.

One thing to double check is that the inverter is happy for you to switch the load side, either in fault conditions or just when stopping / starting the lathe - certainly with older drives I have dealt with this is a definite no-no, though the G110 may well be different. Comments like 'automatic restart facility following power failure or fault' from the Siemens website mean that you need to make sure the inverter is setup right (yep, there are pages of parameters, most of which you can leave at default).

Typically there will be restrictions on the maximum number of stops /starts per hour as well.

HTH,

Chris.

Reply to
Chris

the fuse/MCB rating is the

capacity, not trip current)

fuse/MCB, you would expect

trips the overcurrent

compromising future leakage

So what happens with a whole house RCD, with a live earth fault, the short current could be thousands of amps....?

Reply to
James Salisbury

Hi there,

A few more th> charles adams wrote:

The Quick Start Guide for the Simanics G110 3KW drive specifies a 50A fuse (part number 3NA3820). It also quotes an input current of 35A. The

2.2KW (3 HP) variant specifies an input current of 27.2A

A lot of inverters run with high earth leakage currents on startup (particularly those with EMC filters built in). You may have problems with nuisance tripping on the RCD.

I assume the motor on the lathe is dual voltage (ie 230VAC/400VAC, or

240VAC/415VAC as was)? It will need to be wired for 230V / 240V operation, as most (all?) inverters will only change 1 phase to 3 phase, they won't lift the incoming voltage from 230V to 400V.

I am sure it is obvious but just to clarify things like automatic restart after fault must be disabled.

HTH,

Chris.

Reply to
Chris

In the case of a short-circuit (rather than overcurrent) fault, the large current you mention will flow for only a very short time before being cleared by any one of: the RCD itself (given L-to-E short), the final circuit overcurrent device (MCB/fuse), or the service fuse. So the total energy which flows through the RCD is limited (and it's not just left to chance: this 'let-through energy' is calculated and taken into account in the design of RCDs, consumer units, and supply fuses).

In the case of an *overload* - i.e. drawing more than the rated current, but not massively more or in a way which causes an RCD to trip - the extra load is sustained for quite a long time (given typical fusing characteristics): for example, a 32A MCB will let a current of 40A flow almost indefinitely (hours at least), and will take several minutes at least to clear a 50A overload. So (at least when your loads are capable of causing an overload, which motors sure as hell are!) you need to choose the various elements in the circuit path appropriately. (Now, the people who design RCDs for a living rate them in the knowledge of the characteristics of protective devices they're likely to be used with, and a good-brand '30A load' RCD is likely to be fine long-term with a load protected by a

32A MCB giving rise to occaisionaly overloads; but it's better practice, especially as there's little difference in the price, to use an RCD with a higher sustained-load rating than to push the margins).

Just because it's often the same device (fuse/MCB) which provides both short-circuit and overload protection, doesn't mean they're not conceptually separate, or that it'll always be the one device which does both...

HTH, Stefek

Reply to
stefek.zaba

The 10A will be the continuous rating. When the motor is starting, it will draw massively more current than this.

Best to use 6mm SWA. It may be hard to work with inside a building, but it is easy enough to lay in a trench. Drop to 6mm T&E as soon as you enter the buildings at either end.

6mm will give better voltage drop and more headroom for expansion.

Christian.

Reply to
Christian McArdle

It's an underestimate. 3 HP is about 2.2 kW. When you factor in the motor efficiency (say 85%) and power factor (say 0.8), the circuit loading becomes about 3.3 kVA. 15 amps is nearer the mark.

The inverter may well have a soft-start mode which will reduce the starting current a fair bit.

I'd suggest a minimum of 10 mm^2 for this. It's a fairly long run, 25+ metres from the house, so 30 m of cable, perhaps. The lathe with a 3-horse motor suggests that this is a fairly serious workshop installation. There's probably going to a be at least a bench drill and a grinder, and maybe some electric heating to consider too. A 45 A supply from the house (from a BS

1361 fuse) seems appropriate. The cable size is determined be the need to keep the voltage drop low - you need a good stiff supply from the submain in cases like this, leaving most of the voltage drop allowance avaialble to be used in workshop wiring.
Reply to
Andy Wade

Firstly, thanks to those who have gone to a lot ot time and trouble to respond.

The lathe in question has mechanically variable speed and is further equipped with a clutch all of which mean that the motor will start in isolation from mechanical loads. How much (if any) would this alleviate the cable rating?

Charles

Reply to
charles adams