Potterton Netaheat Control Board

Does anyone have a circuit diagram for the Potterton Electronic Control Board 407676?

Two weeks ago my Netaheat failed to light when instructed to do so by the controller. Turning the boiler stat to off and then on caused the boiler to light and continue working. The following morning same problem and solution. CH is now on continuous - I do not have a roomstat (that's a discussion for another time!) all rads have thermostatic valves. So what can be wrong? As long as power is maintained to the boiler everything works, (and has done for two weeks thankfully) but why should opening the boiler stat contact and then closing them again cause the boiler to fire up and then work correctly? Incidentally I installed the boiler 15 years ago and apart from cleaning and one new spark bracket has worked perfectly until now :-(

Peter

Reply to
Peter Andrews
Loading thread data ...

Hi

had one of these and replaced pcb with one from

formatting link
and replacement worked fine and gave the old boiler new lease of life at reasonable cost - hth

Reply to
NUFFSNUFF

Strange problem but please be careful.. have you a bypass as if not this may trip the high limit when the rads all close off.. Leave one open if you dont have a bypass and on the other hand is the pump over run wired in as if the boiler turns off and the pump over run cannot disperse the residual heat it will also trip the high limit stat. hope this helps

pete

Reply to
gasman pete

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.