replying to daveburton1, delta925 wrote: The OP never updated this thread with the final solution.
I have a Micron 50FF that was fitted in 2004 and been 100% reliable until a month ago.
With no warning or symptoms the indicators were Reset ON, Burner Lit Flashing Slow indicating a software error. No combination of totally removing power and the control knob would clear this.
The fan and pressure switch were tested by independently applying power to the fan and monitoring the switch with a multimeter. The thermistor was measured with the multimeter. As the temperature was more like 5C than 20C a reading of 14K ohm was reasonable. The overtemperature switch was measured and confirmed to be closed. The control valve solenoid coils both measured around 900 ohms.
An advance exchange control board was ordered. The original was a Pijnenburg type 227134 . The exchange was ordered under the same code but a Ritter type labelled
2000227134 was received. The Glowworm website conforms that the original Pektron 801990, Pijnenburg
227134 / 2000227134 and Ritter 2000227142 are interchangeable. It would seem that the Ritter ( the final version ) has been boxed and labeled as 2000801990, 2000227134 and 2000227142 .
Once the control board was swapped the burner lit first time but failed to stay alight. After 3 attempt it locked out. It seems that regardless of the power and control know sequence at least these later boards lock out for a period of time. When the lockout finally could be cleared at the second attempt ( 5 in total ) the burner stayed alight.
While the system was hot the burner turned off then relit controlled by the thermistor without any problem.
However once off for a couple of hours the burner would not stay alight again.
It was at this point a search found this thread.
An electrode had already been ordered in case needed but was delivered a day later. Once fitted the burner lit at the second attempt and has not locked out since.
What this appears to show it that just because an electrode will create a spark it may have deteriorated beyond the point where the burner flame can be detected.
Also possibly the Ritter control board flame detection is less sensitive than the Pijnenburg and / or the electrode deterioration actually caused the control board failure as flame detection errors and lockouts were occurring but not noticed.
While the Glowworm manual fault finding chart can not cover every possibility not showing the burner igniting then the burner being lit as two stages is a major omission. For ' Does burner lit indicator come on ' > no it could say check electrode and wiring, faulty electrode, control board fault.
I hope this helps others with a Glowworm Micron 30FF, 40FF, 50FF and others too e.g. 60FF, 70FF, Halstead Buckingham that use these or a similar control board / circuit board / PCB.