MCB won't reset

Just had an MCB trip.

It's a 6A MCB with only 1 fluorescent fitting on it. Turned off the switch to the light and the MCB would not re-set. I then removed the started for the light and the MCB still won't re-set.

Anyone got an idea what the problem might be?

Reply to
Goonerak
Loading thread data ...

As the switch is off to the light, that rules that fitting out (Unless it has be wired to switch the neutral, rather then the live!)

If this is the only thing on the circuit, then there must be a cable fault, or the MCB is faulty.

Does it trip immediately, or is there a delay?

Have you knocked any nails into the wall recently!?

Any other DIY work done recently?

Sparks...

Reply to
Sparks

Swap it with a working MCB. If that trips, you've got a fault.

Reply to
Aidan

It trips immediately. Was working fine until this evening and I've not done any DIY work that would affect it.

I guess that means it is probably a faulty MCB. Think I will leave it until tomorrow before I try another one ;)

Reply to
Goonerak

Try turning off the main isolator or RCD for this part of the CU, does the MCB still trip then?

Sparks...

Reply to
Sparks

Possibly a faulty switch, or the wiring in the switch box. Make sure there aren't any loose wires in the switch box, such as the incoming line, which may have jumped out and made contact with the back-box. You don't state whether or not you have an RCD as well.

Reply to
Frank Erskine

In >95% of cases it means a fault that draws far more current than the mcb's rating, simple as that. So faulty wiring.

NT

Reply to
bigcat