Unfortunately yes. I've measured a few of these
Unfortunately yes. I've measured a few of these
Quick correction on that. The RCD feeding the Safeblock had tripped. It does get hot - near enough too hot to touch.
That might be the case, but it usually isnt, and we certainly cant assume it is - therefore we can not conclude its safe, and it probably isnt. Therefore a risk is present. If its the PSu case thats that hot. Even if its the TF itself, 60C no load is still a far call from 'we're confident its safe.'
Regards, NT
Some actual results from a 9-0-9 250mA chassis transformer - brand new.
Open circuit after approx 1 hour measured on the top of the clamp - 68 C Approx half load (136 ohm resistors)""""""""""""""""""""""""""""" - 55 C
They do indeed run hot. If its not over 100C its probably safe to run tho - insulation tends to go at 200-400C and most irons start to get dodgy magnetic wise at over 150C.
I agree 100%.
In message , "Dave Plowman (News)" writes
You had me worried with your previous post ;-)
So there you go, small transformers run hot.
I am not surprised by this result.
Thats not a very good design then.. How would the designer know if the transformer was always going to be loaded or not?
Woukd sem to be a bit pointless if not loaed.
Why not leave it out altogether.
HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.