correction - I think the tails could be 25mm², they seem a bit meatier than the earth conductor.

Peter

Reply to
Peter Taylor
Loading thread data ...

Yes, although you may find it cheaper to buy a complete CU with MCBs and then swap the main isolator for a spearately purchased 100mA time delay RCD. Make sure you can get the same make, 100mA time delay RCDs are often not 'off the shelf' items and you may find that it's easiest to find the one of these that you want and then buy a CU to match.

Those ratings seem entirely normal to me. 6A for lighting, 16A for immersion heater or similar, 32A for ring circuits, 45A for cooker or shower. You might want some 20A ones for radial socket circuits.

However MCBs are so cheap now that it may well make sense to get all noew ones which are certain to be correct for the new CU.

Reply to
usenet

I was just going to say seems fine apart from the tails, could do with upgrading to 25mm but there you go. Although the current isn't up to current regs there's nothing that says you have to change the CU. If you have a 30mA RCD as the main incomer then you're covered for faults, the only reason to change is convenience and safety. (See loads of discussions on this type of thing). If it was me I would change it to a time delayed CU.

SJW A.C.S. Ltd.

Reply to
Lurch

"Peter Taylor" wrote | Hope you don't mind if I tag another question on this thread. | I have TT earthing and the CU I fitted in 1984 which has just the one | 30mA RCD (also acting as the main isolator) and 8 Type B MCB's. I | want to change the CU to a split load one, with a 100mA time delayed | RCD and a second 30mA RCD for GF sockets, garage etc.

On a TT system you will need 30mA RCD protection on *all* sockets, not just ground floor and garage.

Owain

Reply to
Owain

Well spotted, missed that bit!

SJW A.C.S. Ltd.

Reply to
Lurch

Owain wrote

Owain, if you've got a copy of the On Site Guide, could you please have a look at Fig. 3a on pages 21/22. The middle diagram is my one, the one with the time-delayed 100mA RCD doubling as the main isolator. The 30mA RCD is fed via the 100mA, and the circuits it serves are labelled "note 2". Circuits fed directly from the 100mA are labelled "note 1".

Note 1 says "circuits to lights, cooker, water heater, smoke alarms"

Note 2 says "circuits to portable equipment outdoors and socket-outlets that may reasonable supply portable equipment outdoors (ground floor socket-outlets)"

It doesn't mention upper floor sockets at all. Am I missing something? Where does it say *all* sockets.

Also Clause 3.6.2 says "Where an RCD is fitted ...... in a TT system, the rated residual operating current should not be less than 100mA". Doesn't this mean that 30mA is too low????

I am getting more and more confused here by the minute!

Thanks for your help Peter

Reply to
Peter Taylor

"Peter Taylor" wrote | > On a TT system you will need 30mA RCD protection on *all* | > sockets, not just ground floor and garage. | Owain, if you've got a copy of the On Site Guide, could you please | have a look at Fig. 3a on pages 21/22. The middle diagram is my | one, the one with the time-delayed 100mA RCD doubling as the main | isolator. The 30mA RCD is fed via the 100mA, and the circuits it | serves are labelled "note 2". Circuits fed directly from the | 100mA are labelled "note 1". | Note 1 says "circuits to lights, cooker, water heater, smoke alarms" | Note 2 says "circuits to portable equipment outdoors and socket-outlets | that may reasonable supply portable equipment outdoors (ground floor | socket-outlets)" | It doesn't mention upper floor sockets at all. Am I missing something? | Where does it say *all* sockets.

I think they've missed something, not you.

Reg 471-08-06 requires *every* socket-outlet on a TT system to comply with

413-02-16.

413-02-16 requires ZsIdeltan < 50V

and

413-02-20 for TT systems requires RAIa < 50V

In practice, you use a 30mA RCD unless you can prove your earth electrode system is and will remain effective. Whitfield simply says that all TT sockets require RCD.

| Also Clause 3.6.2 says "Where an RCD is fitted ...... in a TT system, | the rated residual operating current should not be less than 100mA". | Doesn't this mean that 30mA is too low????

I assume it's talking about whole-house RCDs which should be 100mA Type S time-delay to allow discrimination against the 30mA Type G socket circuits.

Owain

Reply to
Owain

Thats it. I was trying to find the relevant regs. I remember you had to do it, just not why! Being that it would be very unlikely to get the Zs down on TT system far enough to not be able to not use 30mA RCD's then they just get put on all socket circuits. I think it'ws called 'a rule of thumb'!

SJW A.C.S. Ltd.

Reply to
Lurch

Lurch wrote

That's brilliant, thanks chaps. I wonder how many other DIY-ers like me follow the OSG not knowing about this. I will feel happier with all sockets coming off the 30mA - I think I'll put the immersion on it too, in fact everything but lighting & cooker. I don't have a dedicated freezer supply, but I might put one in now after I've done the CU. Presumably that will be a 2.5mm² T&E radial coming directly off the 100mA RCD. Does it need a different type socket or maybe a permanent flex connection?

Peter

Reply to
Peter Taylor

If it's going to be off the 100mA side it would have to be through a fused spur. I think putting the immersion on the 30mA could be asking for trouble. There really isn't any need. I would just have sockets, shower and cooker, if it has a socket incorporated into the switch, on the 30mA. Everything else on the

100mA side.

SJW A.C.S. Ltd.

Reply to
Lurch

Not necessary. This would be a dedicated socket for the fridge and is not likely to be used for any other purpose.

I agree, but putting a cooker on the 30mA side may also be asking for trouble. You could run a 30mA RCBO from the 100mA side of the CU to supply the cooker and prevent nuisance trips.

-- Adam

adamwadsworth@(REMOVETHIS)blueyonder.co.uk

Reply to
ARWadsworth

No, you need RCD protection, but it doesn't have to be as low as

30mA as it's purpose is not protection against electrocution, but as protection against high earth fault loop impedance.

Now some sockets are likely to need 30mA RCD protection to protect against electrocution and you might decide to provide such protection even on sockets where it isn't required by regulations, but a TT system does not require all sockets to have 30mA RCD protection.