Glowworm Swiftflow 100

Swiftflow 100 died today. Main burner not firing on either DHW or CH. Pilot

  • fan + pump running fine. I havent got the installers instructions that would allow me to work through the flowchart that Hepworth thoughtfully include. Before shelling out 115 for a new Gas Valve are there any overheat or flow sensors that would prevent the gas valve operating on both HW & CH ?

Neil

Reply to
Neil
Loading thread data ...

Check the wiring first. You find a one has detached itself or broken. You say the pilot flame is still lit, so this would indicate that the thermocouple is still OK. So check the motorised valves, especially the micro-switches, are making and breaking their circuits correctly, and that all the thermostats are working properly.

If a valve or thermostat isn't calling for heat correctly, then the boiler will not fire up when it should.

Reply to
BigWallop

In message , Neil writes

Is there 24V at the gas valve?

I.e. the question is whether the pcb is delivering the volts to the gas valve or not. It is a common pcb fault, although it could be caused by a sensor failure. You'll find an indication on the pcb as to which connectors they are on.

If it's the pcb, phone me on 01923 229224, you can't look at my website atm as the server is down

Reply to
geoff

Other have mentioned the idea of giving it a good visual once over. Much more likely to fail than the gas valve (IMHO) is the air flow proving switch. I don't know what sort of technology is used on the Swiftflow. Many use a a pair of tubes in the air flow connected to a diaphagm switch.

Reply to
Ed Sirett

If the pilot's OK, then it can't be the APS

Reply to
raden

Sorry I assumed a permanent pilot type.