FCUs/Spurs and powering two outlets

Hi, I'm doing some wiring in preparation for my new boiler which will be going in the loft directly above the airing cupboard. I need to have an 3A DP isolator in the airing cupboard for the boiler, and I also need a 3A DP isolator for the solar water heating control panel. If possible, I would like to power both these outlets from one spur off the upstairs ringmain, although I am unclear as to the exact way of doing this in terms of the number of fused outlets and isolators required.

From reading the regulations, I am allowed to power as many outlets as I want from a spur, providing they are all (as a group) protected by an appropriate fuse. Does this mean I have have to have 3 fuses in the chain, one between the spur and the first outlet (the boiler), then one for the boiler FCU, then one for the solar heating FCU?

This seems a bit OTT so could someone please tell me the correct way of wiring up this arrangement.

Thanks

Luke

Reply to
Luke
Loading thread data ...

On Thu, 12 Aug 2010 04:09:40 -0700 (PDT) someone who may be Luke wrote this:-

Install a fused connection unit at a suitable point in the ring, fuses at 3A. This could be directly on the ring or on an unfused spur that just feeds the connection unit . This doesn't need to be switched, though it will make things marginally easier if it is.

Run a cable or cables from this to the isolators for each bit of equipment .

If you are worried about a fault on one taking out the other then you could use switched fused units for each bit of equipment fused at 3A. You could then use a 13A fuse (or a 16A MCB) at the suitable point on the ring. There is a small value in doing this as then a fault in the boiler should not take out the solar, but if the solar is designed properly it will cope with stagnation.

Reply to
David Hansen