What size conductor should be used to bond everything that's metal to everything else that's metal in the bathroom (but not run back to the CU)?
Cheers,
Mogweed.
What size conductor should be used to bond everything that's metal to everything else that's metal in the bathroom (but not run back to the CU)?
Cheers,
Mogweed.
4mm2 insulated, or 6mm2 bare.
NT
4mm2 insulated, or 6mm2 bare.
NT
Thanks very much NT.
Mogweed.
Correct.
or 6mm2 bare.
Wrong. Bare protective conductors, whether circuit protective conductors or equipotential bonding conductors, are not permitted for sizes of less than 10 mm^2. [See regulation 543-03-02]
HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.