Their seems to be some confusion on the site concerning bonding in domestic premisis, here it is in a nutshell. Main bonding with green/yellow 10mm square (See table 54H of BS 7671 The IEE Regulations) from main earth terminal either in the board or from the supplied main earth terminal link. Connect to incoming gas supply on hard pipes (not lead) within 600mm of the meter and before any tee. Connect to incoming water supply on hard pipes (not lead) on the consumers side of the stop valve and across the meter if one is fitted. A similar connection must be made to any other incoming services such as oil pipes. The connection to the pipes must be made using a bonding clamp complying to BS 951 with a label attached SAFETY ELECTRICAL CONNECTION DO NOT REMOVE. You may loop from one service to another with the bonding lead, but if you do this you must not cut the lead, just strip off the insulation and wrap it around the screw on the clamp. Clean the pipes and ensure tight connections. Get it tested by a qualified electrician.
Supplimentary bonding with 4.0 mm square green/yellow to hard pipes using BS 951 clamps and labels, connect to earth at the nearest socket outlet, immersion heater switch, shower switch or fused connection unit. DO NOT RUN IT BACK TO THE CONSUMER UNIT. If you need more advive get a copy of the On Site Guide (ISBN 0 8526
987 2) around =A317 and read it ALL, don't ignore the bits you don't understand. they know better than you do.