Is there a practical way of providing earth leakage protection for a group of machines fed from a 3 phase distribution board?

My workshop tenant has asked the question as he has someone working on a

*bench space* basis and doesn't want to be sued by a widow.

regards

Reply to
Tim Lamb
Loading thread data ...

well I guess..there is such a thing as a three phase RCD.

Fit it to the bench.

I found several on offer - around 50 quid for a 30mA one.

Reply to
The Natural Philosopher

Tim,

I have several modernish three phase distribution boxes here on the farm all by Wylex. I simply removed the main breaker and replaced it with a compatible three phase RCD one. Conventionally workshop machine are on 100mA rcd trips but I feel happier with all mine at 30mA, particularly as several machines have a standard 13a double socket on them powered from phase 1. To date not had any nuisance trips. Single phase distribution is from a separate box, also with a 30mA trip.

If your distribution boards will not accept an RCD main switch for some reason, just intercept the three phase feed, and bring it via a three gang box with an rcd mounted in it.

AWEM

Reply to
Andrew Mawson

In message , Andrew Mawson writes

Umm... I assumed there would be a problem with starter coils being across only two phases or even phase neutral. Local inspection lighting phase neutral.

The other unknown is DC injection braking on circular saws.

regards

Reply to
Tim Lamb

Yes. See reply to Andrew.

regards

Reply to
Tim Lamb

That is the correct answer (or would be if I was doing the work).

Reply to
ARWadsworth

Thinking about it logically provided all the current that is going into the lines is also all coming back on "safe" lines, all is well. It's when you don't get it all back that you assume it's going to ground, possibly via someone, so you trip the power.

This implies that you monitor the three phases and the associated neutral. How you actually do that I haven't a clue and in delta connected kit there isn't a neutral to monitor, I think. I know enough about three phase to know I'm dangerous...

Reply to
Dave Liquorice

It should not matter... the sense coil is round all phases and neutral. As long as the vector sum adds up to zero, then it can assume all is well. Only when some current returns via a path that does not include the RCD does it trip.

Reply to
John Rumm

OK chaps.

That is clear enough.

Borrowed neutrals would be a mistake but otherwise get on and do it:-)