So the leccy trips out today forcing me to do some investigating. I knew the pond for the socket was wired in 0.75mm2 flex off the back of a socket and had been meaning to disconnect it for some time, so took the opportunity to do so, and the power tripping off was solved.

What I wasn't expecting however was the socket to also be wired in

0.75mm2 flex! We had our fridge and tumble drier plugged into that socket!

Some more prodding reveals one side of our kitcken wired as in the diagram (see the link).

formatting link
3KW tumble drier and outside socket all fed off 0.75mm2 flex. Eeek!

a 3KW kettle, 3KW tumble drier, 1KW toaster, 800W microwave, 250W of lighting, and a fridge all connected off one 2.5mm2 spur. Eeek!

I've disconnected all the 0.75mm2 flex. How would you fix the rest as you are only allowed one single or double socket on a spur.

Only way I can see is to run wire from the last FCU up to the ceiling above, hopefully find where the circuit descends to the socket on the ring and make it a ring again. This would be a right PITA as are floors are chipboard (but might give me an excuse to fix where the floor is uneven in the spare room due to being carved up for what looks like installation of the central heating).

I Thought about putting the spur on a FCU but I think the load is probably too much for a 13A fuse.

I Traced the earth leak to the UV lamp for the pond, so no worries there.

P.S.

The new PCB got our boiler going again thank the lord. Bill came to =A3454 so not as bad as I thought it could have ended up being but still very ouchy.

Reply to
philipuk
Loading thread data ...

If you can't get everything on the ring, can you run back to the CU and wire it as a 20A radial?

formatting link
?

Owain

Reply to
Owain

No, left that job to the boiler man so no idea where he got it from. That was for divertor valve + plate heat exchanger + pcb and about four visits.

Philip

Reply to
philipuk

Makes insurance premiums seem reasonable

Reply to
stuart noble

I think I'd aim for this:

formatting link

Reply to
jgharston

In message , " snipped-for-privacy@gmail.com" writes

what sort of access and how much mess do you want to make? Or are you happy with a 'good enough for now' job? And whilst it's true that only a single fitting on the spur is allowed on current regs, it wasn't always thus, and in reality multiple outlet spurs can be fine unless you hang multiple large loads on them. The wiring here has few for example (old install of course)

I'd start by sticking the spur on a 13A FCU, you will probably find it works fine, it won't blow instantly you get to 13A anyway, and you won't be using all the loads at the same time, though probably a good idea to only put the TD on when you aren't likely to be using the kettle.

Then you can work up to sorting a better job. As an alternative to the ceiling could you go down beneath the work top, either taking out plinth for access underneasth cupboard, or running cable inside the cupboard? to run a cable back to make a longer ring?