The liability aspect is also one of the reasons why no manufacturer will use weaker standards than those specified by the BSI. Installation in an unventilated compartment must have been approved by a relevant standard.
Yes, I have read them. Both parts, about a year ago. Can't say I recall all the detail though. Despite having a copy "in the office", have you read them? But what has that to do with the fact that manufacturers always detail the British Standards that must be complied with when installing? (Besides, the relevant issues governing compartment installation here are covered by 6798 as much as 5440 Pt 2. )
The alternative for these appliances when the additional clearance is not available (i.e. top/bottom vents) is to allow for ventilation. But I would agree that this is not ventilation in the same way that 5440.2 deals, in the main, with ventilation to ensure adequate air supply for combustion.
Manuals sometimes contain misprints, typos and worse (Saunier Duval during the early 1990's were a particularly bad example of this). Therefore, in the event of an apparent discrepancy between the manufacturer's instructions and the standards they are supposed to be compliant with, the responsible thing to do is to attempt to reconcile the two. E.g. by getting the manufacturer to explain how their advice complies with the relevant standards. In the event of an apparent contradiction, to assume that the manual is correct and the standards have been "superceded" is not sensible.
Having said that, I have not yet seen **any** installation manual that on investigation cannot be reconciled with the appropriate BS - as appears to be the case here (I would want to check BS 6798:2000, as opposed to
6798:1987)I will continue to operate based on the Standards **and** Manufacturer literature as:
1) I have never (yet) found a reason to be forced to choose between them. 2) It is clear to me that this is what the manufacturers expect you to use the standards from the frequent references to BS this and BS that in their documents and, in some cases (W-B, SD), a lists of standards that need to be followed.