In my book that IS mis-balanced. One of the things missing from the FAQ is to emphasise that at least one LSV remains fully open, otherwise, as someone pointed out earlier, you can go round chasing your tail.
You need a certain mass flow multiplied by temperature drop to get the design heat out of radiators. It's true therefore that throttling via the LSVs as you suggest will reduce the flow and hence increase the temperature drop. However, this will mean that a greater head is required to overcome the greater resistance you introduce, and the pump may not be able to provide that (a point you yourself make later).
Throttling LSVs and maxing out the pump will most likely produce hissing valves, cavitation etc as mentioned before. A better approach is to reduce the flow rate by slowing the pump down, with at least one LSV wide open. This minimises the required head, and makes for an easier to adjust and quieter system.
For condensation design you want to roughly double the conventional drop across the radiators, to say 20C, which implies halving the flow rate and slowing the pump down. If at the same time you reduce the boiler flow temperature you will get a very low return temperature for your condensing system. Unfortunately you will also have cold rooms in worst case winters, unless you put in larger radiators.
So what to do when replacing a conventional boiler with a condensing one?
1) Ensure properly balanced, with one LSV open to get minimum resistance. 2) Turn the pump down to get larger temperature drop. 3) Turn the boiler flow temp down to get as near continuous burn as you can, as opposed to bursts of firing.A good modern boiler will look after much of 2 & 3 for you.
3) Read Andy's "Nirvana" postsAlternatively, replace radiators with 50% (approx) larger, then do 2 &
On the other hand they do some of the optimising that the majority of home owners have no clue about.
Quite so, and a good reason to keep the system resistance low.
Don't get me going on that.
Phil The uk.d-i-y FAQ is at