Not quite DIY but:
Three phase 415V through RCD/ Breaker unit [3 input terminals, three outputs and one neutral out. Neutral in is via a flying lead [Taken to incoming supply]
From the output The cables go to a six pole contactor.
From the contactor the feeds go to a three element heater block.
6-8kW. The common connection is the neutral which is taken back to the RCD/ Breaker unit.The earth leakage part of the block trips instantly when the contactor is made.
There is no leakage and no connections other than those described to the phases or neutral after the breaker unit.
There isn't a component at fault it seems to be a design issue.
Anyone any ideas?
regards
HN