York Heat Pump and furnace both run at the same time..is this normal?

I have a York combination system with an oil fired furnace and a heat pump. Everything is working fine but I have a question about how the heat pump and furnace work together.

The thermostat is a 2 stage, when the first stage calls for heat, the heat pump alone comes one. If the room temperature drops another degree or so, the second stage calls for heat also and the furnace then comes on. Here is where my question comes in. When the second stage calls for heat and the furnace comes on, the heat pump compressor still remains on. As the furnace heats up, the heat pump condenser input air is getting hotter and hotter. The heat pump is trying to heat air that has already been heated by the furnace. At some point when the furnace warms up enough, the heat pump does eventually shut off , but it seems that it is shutting off due to a high pressure safety or something and that the line pressure is very high at that point. I imagine I can hear the compressor straining to pump heat into the already heated air and I'm thinking this can't be good for the compressor.

Is it normal for a dual system to be designed so that the heat pump and furnace both are operating at the same time or should the controls be wired to turn the heat pump off immediately when the furnace comes on for second stage?

thanks

Mark

Reply to
Mark
Loading thread data ...

It's wired wrong , they should NOT both run at the same time. Get the installer back ASAP to correct the situation and shut off the HP until it's fixed.Switch the T-stat to the Emerg.Heat position and leave the main power on to the compressor

Reply to
kool

Leave mains power to the compressor on ?

Reply to
PrecisioNmachinisT

yup.... compressor heater.

Reply to
Noon-Air

Okay thx threw me off there a sec..

Reply to
PrecisioNmachinisT

Did "HVACguy" wire this for you? Bubba

Reply to
Bubba

re: Everything is working fine...

Based on the responses so far, perhaps that statement was a bit premature. ;-)

Reply to
DerbyDad03

well I've live din the house for 14 years and it has been fine..

I usually use the EM heat setting which is oil only, but with the price of oil such as it is, I am starting to use the heat pump more when it is above 30 deg F outside and I noticed this situation happens occasionaly.

Mark

Reply to
Mark

OK

I have traced the problem to the bonnet sensor. The compressor will shut off when the bonnet sensor voltage gets below 3.75 Volts so the controller works and is wired correctly. But the air temperature out of the furnace and into the condensor gets well above 90 deg F and the bonnet sensor voltage decreases only a little and is about 4.71 Volts when the air is 90 deg F. So I suspect the bonnet sensor is bad. Does anybody know what the temperature vs resistance curve or the voltage vs temperature for the bonnet sensor is supposed ot be so that I can check it. It measures about 34 kOhms at room temperature.

thanks

Mark

Reply to
Mark

Conclusion,,, it's fixed.

I replaceed the bonnet sensor with a 10 kOhm NTC thermistor. It works perfectly now, when the second stage calls for heat, the furnace comes on, when the bonnet temp reaches 91 deg F (and the senor voltage drpos below 3.78Volts) the heat pump shuts off and the furnace continues to run. When the second stage is satisfied, the furnace shuts off. When the bonnet cools down to 89 deg F, (and the sensor voltge raises to

3.83 Volts) the heat pump comes back on. So with the correct bonnet sensor in place, the heat pump never runs when the supply air is above
  1. What I don't know is...if the sensor that was in there was the wrong one from day one or if the sensor went bad. Either way...it's fixed now. Thanks for the advice. Mark
Reply to
Mark

Now....if you actually had a clue...... The furnace heat and heat pump are not supposed to run at the same time. when the heat pump runs, the furnace blower runs only to condition the air. The *normal* air discharge temp for a heat pump is 95F - 105F.

The sensor that tells the system when to switch between the heat pump and the furnace heat is the *OUTDOOR TEMP* sensor.

Here is some more food for thought..... If the furnace heat runs at the same time as the heat pump, it will run the refrigerant pressures through the roof and will eventually do terminal and catastrophic damage to the compressor.

Still think you got it "fixed"??

Reply to
Noon-Air

You need some fresh air. You just "aint right". Bubba

Reply to
Bubba

Depending on the climate conditions, my Trane system, calls for the oil burner to run during the Defrost cycle to keep the air warm to the output plenum because it is actually in the cooling mode.

Reply to
Bumpy

Mark, you did excellent. I am impressed. OK, I know this thread was 9 years ago... I am glad you persisted. Mike

Reply to
Michael Dixon