The nominal answer is no, there would be no harm, because the power drawn is determined by the appliance, not the circuit breaker. However, some equipment may not be adequately protected against overload or fault if it depends on the circuit breaker for overcurrent protection. Check whether the smaller equipment has built-in overload and overcurrent protection.

If you want to be a bit more sophisticated, install a small sub-panel with one circuit of each rating at the location of the equipment.

Reply to
RMUH
Loading thread data ...

rather than run two new lines for two new pieces of equipment, i would like to run just one line and share the new outlet given that i would never need to use the two pieces of equipment at the same time.

one of the pieces of equipment i want to hook up is rated as 1p, 240v,

47a and came with a 6-50 plug. the other piece of equipment is rated as 1p, 230v, 28a and came with a 6-30 plug.

my plan is to run a dedicated 50a line which would accommodate the 47a (6-50 plug) piece of equipment. i then want to change the 28a piece of equipment's plug from 6-30 to 6-50 so that it will also fit into the new 6-50 outlet.

would this create a hazard and/or damage my 28a piece of equipment?

Reply to
aeneas1

AS long as you wired the plug correctly you will be fine. The device will only use the current it needs.

Reply to
Ralph Mowery

In reality you will be running a dedicated 60A line, since you have to run # 6 wire, which is rated for 60 amps. You can't run #8 wire because that is rated for only 40 amps.

Keep in mind the 28A equipment might need a different breaker for protection. Consult with the manufacturer. What kind of equipment are we talking about?

Reply to
Mikepier

Please correct me if I'm wrong but are not the breakers meant to protect the wiring from the breaker to the load? Any load device protection provided by the breaker is just by accident?

Load & circuits do tend to be balanced but isn't that mostly a cost consideration not safety?

Kind of silly to run a 60 amp 220v circuit when a 30 will do?

How often do we plug a 1 or 2 amp appliance into a 20 amp breaker, no load protection here.

cheers Bob

Reply to
BobK207

Did you read the original message, or just the title? (I'm not being sarcastic; the original message was posted several days ago.) He wants to install a 50A outlet and switch back and forth between plugging a 50A or a 30A appliance into it.

The biggest problem I see is the contacts in the outlet might wear out from all the plugging and unplugging. Then they would overheat someday when the higher load was plugged in.

I'd either run a seperate circuit for each, or (if maybe I didn't have enough extra spaces in my panel) run a 50A or 60A branch circuit with both a 50A outlet and a 30A outlet (30A devices are rated 50A.) Protect the 30A appliance by installing a fused disconnect or switch just before the 30A outlet. A switch for disconnecting large equipment in case of a fire without having to pull the plug is a good thing anyway.

He might also look at the very specific tap rule for installing an electric oven and electric cooktop on the same circuit -- it doesn't literally apply here, but...

Best regards, Bob (no relation)

Reply to
zxcvbob

You're correct, I didn't read the OP very carefully.

I missed the plug / unplug idea, which isn't great but does prevent simultaneous use.

Switching the load would guarantee not over loading the breaker but his best bet is two separate circuits.

Having both loads plugged to separate outlets feed by the same circuit would allow a potential overload condition.