Hi. I'm laying out my basement lighting. I expect to have 25 recessed lights, each is 75watt max rating (even though I will use LED, I know I must still assume max rating of fixture). 25x7575watts/120V = 15.6amps. So, I cannot use one 15amp breaker and 14awg wire. Can I wire all the lights with 12awg and a 20amp breaker? All comments appreciated.
Thanks Theodore
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 9/27/2015 6:31 PM, snipped-for-privacy@yahoo.com wrote:

Are these in *one* room? Does this one (proposed) lighting circuit represent the entire basement? Are they all controlled from a single switch? Are they arranged in one long (electrical) "line" (i.e., the 25th lamp being the farthesst electrical distance from the supply)? What's the longest "electrical length" encountered? Have you guesstimated what the voltage drop will be at each fixture? Have you considered what you will rely on for lighting if/when that circuit is "off"?
Typically, a (lighting) branch circuit is sized at 80% of its load.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Sorry, I should have described more. These lights are in 4 separate areas/rooms of the basement, on 4 separate switches. Approx 6 lights per room/switch.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 09/27/2015 09:29 PM, snipped-for-privacy@yahoo.com wrote:

Safety considerations aside, I'd put the lights on several circuits, you would not want your basement to go completely dark if a breaker tripped.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 9/27/2015 7:29 PM, snipped-for-privacy@yahoo.com wrote:

So, when the circuit trips, you're completely in the dark (?)
Usually, you try to arrange to have an alternate source of light/power adjacent or nearby -- so you're not left in the dark. I like to have an adjacent room on a different branch circuit so I can let light stream in through an open doorway, etc.
Also, have you considered using LED *fixtures*? Using an incandescent fixture with an LED replacement bulb ties you to the VA rating of the fixture, not the bulb within. Using an LED *fixture* lets you get away with less.
I haven't looked at the transient characteristics of LED lighting to know what sort of "surge" they impart to the line. Presumably, they have been designed with the characteristics of incandescent counterparts in mind? (i.e., I wouldn't want to end up welding the switch contacts together from some start-up surge owing to capacitors in the lamps)
Lighting tends to be considered a continuous load so the branch circuit must be sized at 125% of that load (said another way, you can only "use" 80% of the rated circuit ampacity -- 16A for a 20A branch circuit).
If you put an outlet on the same circuit, then the rules change.
You also have to look at *where* the load is located. Putting a 16A load on the end of 100 ft of wire will result in a voltage drop of ~6.5V at that 100 ft point. The maximum *recommended* allowed voltage drop on a branch circuit is 5% (6V for 120VAC). The maximum recommended drop AT THE FAR END OF A BRANCH CIRCUIT is 3%.
[#12 AWG is considerably more annoying to work with than #14 AWG. You might want to keep that in mind]
And, of course, *local* code requirements trump the NEC all the time. (I lived in a place that required EMT for all runs!)
Have you cornered anyone at your local electrical supply house to see what sort of "free advice" they offer? (which you will take with a grain of salt...)
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sunday, September 27, 2015 at 11:10:28 PM UTC-4, Don Y wrote: circuit so I can let light stream in through an open doorway, etc.

That would seem to be the best observation. OP is worried about 75W times X number of fixtures, etc. For new work, the obvious solution today is an LED fixture that is just that and won't accept an incandescent.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sun, 27 Sep 2015 19:29:09 -0700 (PDT), snipped-for-privacy@yahoo.com wrote:

The code says you will be fine, general lighting circuits in the US are based on square footage, not the number of outlets. YMMV in the great white north.
If you think you would ever have all 75w lamps and all of them will be on at once, by all means go with the 20a circuit but that is a design decision not a code decision.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sun, 27 Sep 2015 18:31:43 -0700 (PDT), snipped-for-privacy@yahoo.com wrote:

No. You are limited to the number of "devices" on the circuit Generally accepted as 8 on 15 amp and 12 on 20 IIRC.. I'd wire it on 2 circuits, with either 2 rings, or rows, or every second lamp on opposite circuits. I'd use an edison circuit,or at least a double (120/240) breaker powering a 2 pole contactor controlled by a single switch if you want all lights on at once all the time. I have an application where 3 circuits are controlled by a 3 pole (3 phase) contactor controlling 3 circuits of lighting on one switch - 12 potlights per circuit, 20 amp breakers. Originally 75 watt incandescents, currently running 9 watt LEDs.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 9/27/2015 7:09 PM, snipped-for-privacy@snyder.on.ca wrote:

That applies to *outlets* (180VA per single/dual), not circuits that are used exclusively for hardwired lighting devices.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
That applies to *outlets* (180VA per single/dual), not circuits that are

Understood. This would be a dedicated lighting circuit, or circuits. Absolutely no outlets on it. Outlets will have separate circuit(s) and breaker(s).
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sun, 27 Sep 2015 20:32:23 -0700 (PDT), snipped-for-privacy@yahoo.com wrote:

Not to be pedantic but any termination of a circuit where energy is used is an "outlet". not to be confused with a "receptacle" where you plug things in or a "lamp holder" or "luminaire" where you install a "lamp" (AKA light bulb). Those are just types of outlets. A "device" is a piece of equipment that does not consume energy, like a switch, breaker or any of those other little pieces of hardware in an electrical installation like the wire nuts, connectors etc. The lamp holder itself is a device but the location is an outlet.
If we are going to talk code, lets speak the language so nobody gets misinformation. ;-) The reason why you get away with having all of those lighting outlets on one circuit is 210.23(A)(2) specifically exempts "luminaires" (AKA light fixtures) from the fixed in place equipment. You also have the protection of 240.4(D) (AKA idiot protection) that artificially derates 14,12 and 10 gauge wire so the breaker is only 80% of the actual conductor ampacity. Your 80% protection is built into the 14a breaker on 14 gauge wire, which is actually 20a wire in 310.16.
They know nobody actually reads those labels and you may use LEDs, CFLs or you might screw in 150w PAR-38s. The breaker will trip before the wire overheats. Being in the dark is another "design issue" not a code issue. Personally I would split them up but I couldn't make someone do it with a red tag. The same is true of loading too many outlets on a circuit. The code just says you have to allow 3VA per square foot in residential but it is not specific about how you wire it other than the ambiguous "Load Evenly Proportioned Among Branch Circuits" in 210.11(B). That is hard to determine until you see how the homeowner arranges their furnishings and equipment so it is pretty much meaningless.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Point taken and agreed. To summarize and rephrase: the subject is a lighti ng circuit(s) on which there will be 4 groups of luminaires (one group in e ach "room" of the basement, and each group having 4-6 luminaires), and each group is activated via separate switches; and NO receptacles will be insta lled on this/these dedicated circuits.
And it seems that even though it is NOT prohibited by the NEC, the concensu s is that I should split this into two 15amp lighting circuits for two reas ons: easier to work with 14awg, and better design such that a tripped break er wont plunge the entire basement into darkness.
Did I get all that right? :) All comments appreciated.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 28 Sep 2015 06:38:07 -0700 (PDT), snipped-for-privacy@yahoo.com wrote:

Yup, legally it could all be on a single 15 amp circuit but that might be a bad "design" decision.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Point taken and agreed. To summarize and rephrase: house is located in New York, the subject is a lighting circuit(s) on which there will be 4 groups of luminaires (one group in each "room" of the basement, and each group ha ving 4-6 luminaires, and each luminaire being rated at 75watts by its manuf acturer), and each group is activated via separate switches; and NO recepta cles will be installed on this/these dedicated circuits.
And it seems that even though it is NOT prohibited by the NEC, the concensu s is that I should split this into two 15amp lighting circuits for two reas ons: easier to work with 14awg, and better design such that a tripped break er wont plunge the entire basement into darkness.
Did I get all that right? :) All comments appreciated.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Point taken and agreed. To summarize and rephrase: house is located in New York, the subject is a lighting circuit(s) on which there will be 4 groups of luminaires (one group in each "room" of the basement, and each group ha ving 4-6 luminaires, and each luminaire being rated at 75watts by its manuf acturer), and each group is activated via separate switches; and NO recepta cles will be installed on this/these dedicated circuits.
And even though the NEC does not prohibit me from wiring this via 12awg and one 20amp breaker, the concensus is that I should split this into two 15am p lighting circuits for two reasons: easier to work with 14awg, and better design such that a tripped breaker wont plunge the entire basement into dar kness.
Did I get all that right? :) All comments appreciated.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Monday, September 28, 2015 at 9:52:28 AM UTC-4, snipped-for-privacy@yahoo.com wrote :

ew York, the subject is a lighting circuit(s) on which there will be 4 grou ps of luminaires (one group in each "room" of the basement, and each group having 4-6 luminaires, and each luminaire being rated at 75watts by its man ufacturer), and each group is activated via separate switches; and NO recep tacles will be installed on this/these dedicated circuits.

nd one 20amp breaker, the concensus is that I should split this into two 15 amp lighting circuits for two reasons: easier to work with 14awg, and bette r design such that a tripped breaker wont plunge the entire basement into d arkness.

I believe GFRE who's the authority on code issues, said that you can put it all on one 14 amp circuit if you want to. I agree with two circuits being marginally better though, from the blackout standpoint. But I can't recall a breaker here ever tripping on a circuit that is dedicated to lighting. I can recall plenty of cases where the utility has gone down, plunging everything into darkness. Since that's survivable and in my world actually occurs with some frequency, the additional benefit of having two lighting circuits is a nit, IMO.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 28 Sep 2015 07:14:38 -0700 (PDT), Uncle Monster
Excellent idea for anyone.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 28 Sep 2015 16:10:27 -0700 (PDT), Uncle Monster

I still have one of the old school battery lights with the big incandescent floods When the battery dies I may look at a LED replacement although if I just put LED bulbs in there, it would last forever on the battery.
I do have a switch in it that puts the lights in series if I want and makes the battery last a real long time. That is still plenty of walking around light.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 28 Sep 2015 20:19:01 -0700 (PDT), Uncle Monster

No I haven't actually looked.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sun, 27 Sep 2015 20:11:09 -0700, Don Y

... and only applies in commercial in the US