Wire extension

I have added a sub panel to the main so that I can increase the number of circuits. To do this I had to move two of the existing breakers to the sub panel. This was done so I could install a 60 amp double breaker to feed the sub panel. The existing wires leading into the main panel were too short to reach the sub panel. I extended them using twist-on connectors in the main panel. This works OK and all outlets have correct polarities, etc.
My question. Is this an acceptable method of extending the length of existing circuit wires? If not, how should this be done?
Many thanks.
Peter.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
It would have been better to remove the wires entirely from the main panel and install a junction box or two nearby and extend the wires from the junction box to the subpanel. It is not always acceptable to use the main panel as a junction box.
John Grabowski http://www.mrelectrician.tv

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Not exactly true there are residential panels produced today that have a "rated wire way" in the UL listing for this very purpose.
You will need to check with the panel manufacture.
I would recommend if the panel is not have a rated wire way then remove the wires and put them into a junction box with a blank cover. Label the cover as to what the circuits are.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
I think you've gotten a couple of accurate responses to your question. Being the curious type, I'd like to know why you're asking if, as it sounds, you have already done the work? Is something or someone giving you problems? This kind of quest is usually asked beforehand.
Regards, PopS
:I have added a sub panel to the main so that I can increase the number of : circuits. To do this I had to move two of the existing breakers to the sub : panel. This was done so I could install a 60 amp double breaker to feed the : sub panel. The existing wires leading into the main panel were too short to : reach the sub panel. I extended them using twist-on connectors in the main : panel. This works OK and all outlets have correct polarities, etc. : : My question. Is this an acceptable method of extending the length of : existing circuit wires? If not, how should this be done? : : Many thanks. : : Peter. : :
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Agreed, and I shall install a blanked junction box ASAP.
True, I already have done the work using screw-on connectors. But now I have had second thoughts and it is no big deal to do it right.
Peter.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 12 Sep 2005 17:19:25 -0400, "PVR"

Dan, and yes I am a residential electrical inspector.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 12 Sep 2005 09:23:24 -0400, "PVR"

Wirenuts work but there are better splicing methods for big wire. Look at Ilsco.com (or whatever it is) There are other companies and they do make some pretty insulated splicing blocks
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

He never mentioned big wire -- he said he had to move 2 branch circuits -- so most likely it's 14 or 12 gauge wire.
-Tim
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 12 Sep 2005 21:47:43 -0500, "Tim Fischer"

I was confused with the "60a", you are right, there is nothing wrong with a wirenut for 15 and 20a circuits. Sorry for the confusion.