In preping house to sell was running dedicated circuit to bathroom for gfi socket as bathroom had no socket only only light switch. discovered that all upstairs (bathroom and 3 bedrooms) were on 2 (two) 20 amp breakers that were ganged. Also found the old wiring was 14 gage. I will of course be replacing the breakers with 15 amp breakers. Anyone have any idea why the breakers were ganged and when replaced must I also use ganged 15s or just one for each of the two circuits?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Thu, 21 Jul 2005 23:17:28 -0400, " snipped-for-privacy@nospam.net" <uriah> wrote:

There is a chance that those two circuits are sharing a neutral (an Edison circuit). It is a good idea to keep them ganged so that no one will accidentally but them on the same "phase" in the future.
Steve B.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
How do I check for this type circuit?

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
"Normally" there will be a red wire to one breaker and a black wire to the other. And "normally" they will trace to a common cable with a single white.
I suppose the acid test is to read the current going out over the two hots and the current returning over the (presumably) single neutral. The neutral current would be the difference between the two. <uriah> wrote in message <uriah> wrote:

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Trace the two wires back up the panel to where they enter and see if you are dealing with on cable (two hots, one neutral and probably a ground all in the same jacket) or two separate cables.
If you only have one neutral then it is an Edison and should be on a ganged breaker but there is no requirement to do so. The reason it is a good idea is that current on one leg balances out the current on the other leg so if you have 15 amps running on one leg and 10 on the other the neutral is carrying the difference of 5. If you accidentally got both breakers on the same leg then the balancing is gone and now you have 25 amps running back over the neutral which is more than it would have been rated for.
Steve B.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@nospam.net wrote:

Do you have electric heaters on those circuit? I would suspect that someone ganged the breakers with two wires instead of using one heavy wire.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

He said:

Doesn't sound like these are heating circuits, but General purpose ones.
Either there's a shared neutral, or the wiring from both circuits goes into a common junction box (which doesn't require ganging, but some people do for safety), or someone was stupid -- after all they missized the breaker so they could have mis-applied it as well.
-Tim
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
No electric heaters.
On Fri, 22 Jul 2005 04:12:20 GMT, "George E. Cawthon"

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@nospam.net wrote:

If the two circuits are both going to the same outlet, then the breaker should be ganged. (From what I have read) If not then someone probably just used what was available. But I wouldn't ungang them unless you can map out the circuit 100%.
--