I'm looking into getting a Weil-McLain Ultra Boiler installed this Spring. I've done research on it, and came across a quote that bothers me a little: Someone saw it at a home repair trade show and said that it never shuts down, it modulates up and down. Now, does that mean it never shuts down AT ALL, even when the temp gets to what the thermostat is set at; or that it never shuts off while the heating system is running, and goes off when the thermostat doesn't need anymore heat? I've assumed the latter is true, but it wouldn't hurt if someone who knows this system confirms that. Thanks.

Mike

Reply to
Michael Gallagher
Loading thread data ...

It will shut off when the demand is low enough. There is a minimum safe flame level on any burner system below which the gas valve must shut down. During periods of high demand, e.g. cold outside, it may very well run continuously. The Ultra regulates air/fuel mixture to maintain high efficiency burn. It's actually higher in efficiency at low fire, which is one good reason to have a modulating valve.

hvacrmedic

Reply to
RP

Modulating is the way to go. Most boilers fire the burner at a pre-set temperature, the water temp comes up and the burner shuts off until it drops to another pre-set, the starts up again. Modulating boilers work by closing down the gas and air to make a smaller flame once a certain temperature is reached and opens up more as the temperature of the water drops. This is more efficient and keeps a more even temperature.

Once the temperature gets to high in very mild weather, it will shut the burner off

At works, we have three modulating boilers for high pressure steam that work the same way. Works well and I'd not want it any other way.

Reply to
Edwin Pawlowski

Just so I'm clear on this, "demand is low enough" means "the temp gets to the setting on the thermostat," right?

Sorry for seeming to somewhat anal, but this thought came to mind: The Ultra's fuel efficency wouldn't do me much good if it runs 24/7!

Mike

Reply to
Michael Gallagher

The t-stat doesn't operate the boiler. The boiler will maintain an a preset outlet water temp to the best of its abilities via an adjustable internal temperature control. The internal control modulates the gas valve in response to changes in water temp. The colder the water gets the more the valve opens. The valve will thus raise or lower the burners in response to the demand put on the unit. This is, believe it or not, much more efficient than simply cycling the valve on and off with a conventional thermostatic on/off control.

It won't run constantly all the time, only when there is a high demand put on it, but still no worries. Depending upon water temperature setpoint, the burner may or may not cycle completely off between calls for heat at the t-stat. There are several factors involved, including whether or not the boiler is being used for central hot water in the house, whether hot water is being used to take a shower, wash clothes or dishes, etc during the heating system off cycle. The boiler system is designed to modulate the flame height in lieu of cycling off. Excessive cycling kills burner efficiency, as the air/fuel mixture and stack flow attempt to stabilize. In addition at low fire more of the heat generated gets transferred to the water. Modulating the flame to a lower level prevents cycling for the very purpose of *increasing* efficiency. Though it may run longer at low fire, it is using less gas while it is running. The end result is a net fuel savings.

hvacrmedic

Reply to
RP

Right. actually, it is more complex than that but no, it will not be running 24/7. You will probably see less fluctuation in the temperature also as the boiler modulates and decreases the output at times.

Why not? Why do you care how long it runs if it is saving you money. A roaring forest fire will put out enough heat in a minute to keep your house heated for a season. Do you think that is more efficient than running a candle 24/7?

Reply to
Edwin Pawlowski

Thanks for clearing that up.