Using Performance Data Spec Sheets to figure - Condenser Temp-Split
Testing whether the A-C System is delivering the Manufacture's BTUH Rating by checking the Condenser's Delta-T
For the uninitiated, Delta-T is the difference between the air temperature entering and leaving the outdoor A/C condensing unit. This is a good diagnostic check because it measures the latent heat of condensation as well as the sensible heat absorbed by the vaporizing refrigerant in the indoor evaporator coil. I'm betting when you find out approximately how many BTUH the A/C system is actually transferring outside, you may be shocked.
CONDENSER TEMP-SPLITS
18,400-btuh 17.7 Temp-Split 2Ton 24,800 22.8-F Temp-S 2.5T 30,200 19-F Temp -S 3 T 35,600 16-F Temp -S 3.5T 42,500 18-F Temp -S 4T 48,500 18-F Temp -S 5Ton 59,000 22-F Temp -SBy using the various units' base specification sheet data from the dealer, you can determine if it is operating near its BTUH capacity rating.
The Base Spec sheets 12-SEER part no. 421 41 33301 03, Feb 2001. These are the Comfortmaker® units, which are nearly identical to Heil® units. While the "Performance Cooling Data" is listed at a 95-F outside ambient temperature, you can adjust the indoor airflow to get the Nominal BTUH Rating at the customer's normal indoor stat' temp' setting and most outside temp' operating hours.
The compressor's Service Factor will handle the electrical load as long as the discharge gas temp doesn't get above 225-F. The amp draw can vary from 5.7 to 10.7 amps on my Kenmore window unit's spec sheet. The nameplate rating is 7.5 amps at 115 volts, 10.5 that's 5 amps above the rating, or 28½ % above the nameplate rating. [1.3 SF] It will handle up to a 120-F outside ambient.