In my breaker box, I have two 40A breakers side by side. One is for the A/C, one is for the electric dryer.

Seemingly simultaneously, both of them experienced a loss of power (around

11V) on one leg. Thus, neither the dryer nor a/c work.

Can anyone imagine how this could happen, seemingly simultaneously?

H
Reply to
H
Loading thread data ...

What do you mean "on one leg"? I'm assuming that the power to both the A/C and dryer is 220V.

Reply to
Travis Jordan

I assume you have two 40A double pole breakers side by side, is this correct? 11V L1 to L2? 11V L1 or L2 to N? Please provide some more details.

Reply to
Eric9822

On a 240V circuit, each leg is 120V (or more).

Reply to
H

Yes, there are two 40A double pole breakers side by side.

On both, at the breaker, it's 240V on both.

At the other end of the line, it's around 80V (combined) on both. One leg has 127V, the other measures between 11V and 18V.

Reply to
H

Only way I can imagine this happening simultaneously is if one transformer phase on the utility pole went out. Have a look at your power meter - is the disk turning at all? If you feel safe doing so and have a decent voltmeter, you could open the service panel and check for voltage between the bus bars. Check each bus bar to the neutral line, and to each other; there should be 115 volts between each phase and neutral, and 230 between the two bus bars.

If there's not, you have a problem. My own inclination would be next to check at the terminals right on the master breaker, if they're accessible (not easy on some designs), on the house side; if you still have a loss of voltage, then I'd check on the other side of the breaker. If the problem exists on both sides of the breaker, call the hydro company. If the supply side is good but the service panel side isn't, call your favourite electrician.

WARNING: Don't do this if you are at all unsure of what you're doing! Wear electrical safety gloves rated to at least 1000 V, long-sleeved shirt and trousers (sleeves rolled down), rubber-soled boots and stand on a piece of rubber mat while you do this. Have someone stand by with a

3 or 4-foot length of wood - 2x2 will do nicely; if you have an unfinished (i.e., not varnished or painted) wooden cane, even better. Their job will be to knock you clear of the panel if something happens and you accidentally contact something.

Sorry if this is stuff you already know, but better safe than sorry - and it may be of use to others.

Yours aye, W. Underhill (who, the other day, proved the axiom that familiarity breeds contempt and as a result was bitten by 440 V on an auxiliary relay...)

Reply to
William Underhill

Well, I do know what I am doing around a breaker panel, but I had an electrician anyway testing the breakers. They are working perfectly. Full power on the business leads of the double breaker. The other end (at the dryer and A/C) is where the problems manifest themselves.

One thing of possible import: I am having a new room added to the back of the house, and an electrician ran a new wire into the breaker panel, though he did it rather blind (he could not see exactly where the drill came out in the basement.

It seemed to me that had he hit the 240V line, sparks (or something) would fly. None of that happened. But, if he had nicked both 240V lines, would that explain the power loss (which is not total)?

Reply to
H

It sounds like you lost one pole of each double pole breaker. Just loosing

11 volts wouldn't stop it from working. If you lost one pole of each of those breakers you probably lost one leg of the main breaker or the entire service. In a modern breaker panel, there is pretty much no way to loose one leg of just two breakers

Reply to
RBM

Both breakers are working perfectly.

Reply to
H

So, you didn't lose any voltage at the breakers as you first indicated?

Reply to
RBM

I reread what I originally typed, and guess I sent the message too soon.

Yes, the breakers are fine and the power in the breaker box is fine.

The problem is at the other end of the line.

Reply to
H

Each of the two double pole breakers reads 240 volts at the breaker, but something less at the dryer and at the AC. What exactly is the reading across the two hot legs at the dryer and the AC?

Reply to
RBM

L1 to L2 around 80V L1 to N - 127V L2 to N - 11V

Reply to
H

It's the same at the air as the dryer? Are these breakers new or existing? are they full sized breakers or mini breakers?

Reply to
RBM

Is that after the breakers? Sure isn't much else in you panel that could be faulty.

Reply to
Meat Plow

Same at both.

Full size breakers. Both are working perfectly. Each breaker is about 5 years old (after a heavy up).

Reply to
H

Are the cables that go from the breakers to the dryer and airconditioner continuous, or are there junction boxes

Reply to
RBM

In theory, continuous, but they were laid 40 years ago, and I cannot see exactly where they go.

Note that they were working perfectly until about a week ago, and simultaneously failed.

Reply to
H

It sounds like you lost one leg of each cable, but I can't imagine how that could have happened. At this point you'd need to disconnect each cable from the breaker and at the load end, and do a continuity test to verify each conductor

Reply to
RBM

Already done, and there is continuity, but the power down the "bad" leg is bad.

I'll tear apart the wall near where the electrician ran the new wire, and see if he possibly nicked both of the lines.