I have a question about NEC regarding a situation I discovered in my house. I was adding a new circuit for a shop light in my garage when I came across some 12/3 Romex that was powering some fixtures in the ADU that is attached to it. There are two lights in the bathroom of the ADU, one vanity light and one fan/light combo. They were running from a run of 12/3 romex, but wired in such a way that each had its own hot cable (one black, one red) and were sharing a common ground and neutral. Each had a 15A breaker back in the box. My first question is, is this allowable under NEC? Since it seems overkill to have a whole 15A breaker for each light, I was wondering if I could just run each hot (black and red) from the same 15A breaker? Or should I just rip it all out and run them in series on some 12/2 Romex? I have a little quick reference book about NEC but it doesn't mention anything about this.

Big 8' shop lights turned out great though!

Thanks!

-JDS

Reply to
JDS
Loading thread data ...

According to JDS :

Look for "Multi-wire branch circuit". Yes, they're legal. I prefer that the breakers be tie-barred, but in this case they don't need to be under NEC. (Under CEC they do).

You could.

Reply to
Chris Lewis

You could if the breaker is rated for two wires; otherwise you can pigtail them; but that is ugly. Only problem might be that someone in the future might assume it was a properly wired multiwire circuit.

>
Reply to
toller

What is ADU?

If the fan light has a heat lamp in it, a separate circuit might be a good idea.

Reply to
SQLit

If the two 15A breakers are on opposite sides of the incoming 240 (an Edison circuit), then the current wiring is OK.

What you suggest is OK from a safety standpoint, but why? The current setup works and is code (I'm assuming). Tying the red/black together is going to create a potentially confusing situation, since the usual assumption is "1 conductor = 1 breaker capacity", and you're violating that assumption.

Reply to
Andy Hill

You must make sure that the two breakers are on opposite legs in the panel; in most panels this is the case if the breakers are next to each other. This makes sure the current cancels out in the neutral instead of adding.

It does seem like overkill, doesn't it. To have the bathroom *outlet* on its own breaker would make more sense.

Chip C Toronto

Reply to
Chip C

Hey all, sorry about the direct replies. I meant to reply to the group.

Thanks for all the help.

-JDS

Reply to
JDS

Attached Dwelling Unit.

Not a bad idea..

Reply to
Bob Vaughan

Currently the ADU wall outlets are all on one circuit, this includes the single outlet in the bathroom, so I am in violation right there I guess. From what I understand about code when someone renovates is that if I start messing around with it, I need to bring it all up to code. So maybe I should run a dedicate 20A circuit to the bathroom for the light, light/fan and outlet. Better bust out my fish tape!

-JDS

Reply to
JDS

(Chip C said:) "You must make sure that the two breakers are on opposite legs in the panel; in most panels this is the case if the breakers are next to each other. "

I have the same situation in 4 circuits of my house. In both cases the red and black hot wires run to 1/2 size breaker paired with another in the same slot. Can I assume when using these double 1/2 breakers, each of the branches is on the opposite line?

Reply to
AutoTracer

Do yourself a favor and run a new twenty ampere multi wire branch (Edison) circuit to the bath room. One leg will be the receptacle the other will be the bathroom heater. One eighteen hundred watt hair dryer is the entire ampacity of a fifteen ampere circuit. Even an electric tooth brush recharger would be enough additional load to trip a fifteen ampere circuit breaker. One you get the heater and plug of of the other circuit the light bulbs probably won't be enough to worry about.

Reply to
HorneTD

If those half width breakers are really in the same slot then those two circuits are improperly wired. As another poster has suggested you should use a meter or voltage indicating tester to make sure that there is 240 volts between the load (output) terminals of the breakers that share a neutral so that the two loads balance each other and reduce rather than increase the load on the shared neutral.

Reply to
HorneTD

According to toller :

Most of the breakers I've worked with are rated for two. The ones with metal plate "washers" that clamp the wire would all be.

I should point out that "workmanship rules" (ie: comments in Knight) say "only one wire in the panel per breaker".

Yeah, pigtailing is ugly. I hates it ;-)

If you were going by what you saw in boxes _other_ than the panel, you'd assume the red to be part of a switch circuit (ie: three way, or certain other arrangements such as switched outlets). As such, I don't think there's likely to be an issue. I don't think the NEC/CEC cares. It might be more of a "workmanship" issue, but I don't think you'd get much resistance from an inspector on rearranging an _existing_ circuit.

In other words, you'd be okay with reworking existing wiring, but you shouldn't do "new" this way.

Reply to
Chris Lewis

I will check but the point is moot anyway since I plan to upgrade to a 200A panel and change everything to fullsize breakers. My Zinsco panel is not the best to begin with, Cant even get AFCI breakers

Reply to
AutoTracer

Great idea! I can just rewire the existing wire and leave it in place. Put the lights and fan on the on leg and the plug on the other.