Turn off a heat pump toaster?

Is there a way to turn off the emergency heat (resistance heater) in a heat pump system. Mine is a TRANE system heat and A/C in one using. I want to be able to turn it on and off whenever I want and not have the toaster kick in.

Thanks for any tips. There are 6 breaker switches on the side of the unit, no labels though.

DeanB

Reply to
dean
Loading thread data ...

Mine was wired so you could disable the strip heaters for normal heat-up. They would still come on during the defrost cycle. You can just turn off the breakers to the strip heaters ( that will be the high current ones probably), but you will get blasted with cold air during the defrost cycle. My heat pump had

30 amp breakers for the compressor and fan, and 60 amp for the strip heaters.

Bob

Reply to
Bob F

I had a 60 and a 30 amp breaker for my air handler.

Unfortunatley the 60 amp also powered the fan and the control transformer.

I "re-wired" the air handler so that the 30 amp took on the transformer and the blower motor plus 1/3 of the strip heaters. (We have "dumb" controls on our system but even if you have a "smart" controller anyone who can read a circuit diagram should be able to transfer the load from one breaker to another.

I found that the defrost cycle with only one bank of strip heaters wasn't all that bad. For one thing, the strip heaters don't come on all at the same time. They are usually switched on by "thermal relays" and these relays have a built in time delay. I suspect that the strip heaters are sized to inside temperatures "comfortable" on a VERY cold day. That's "overkill" in my mind. In VERY cold weather I would rather put smaller heaters in occupied rooms and let the "background temperature" fall to the

60s (or below) range. Maybe I would feel differently if we routinely had below zero (F) temperatures for weeks on end but that's not the case here in Tidewater Virginia.

Were my backup generator a little larger it could carry the heat pump. If that were the case, I would wire in a switch or two to keep the strips from coming on either from thermostat demand (emergency heat or stage 2 heat) or from the defrost board of the heat pump itself. But my generator isn't quite up to heating the house so there is no point.

Reply to
John Gilmer

All you have to do is disconnect the wire from W2 on the thermostat. If you want to be able to turn the aux heat on and off at will, put a tiny toggle switch wherever you can mount it to the thermostat and run the wire from W2 through it. Personally, I would leave it so that it does come on during defrost though. I have two old Trane heat pumps with gas(propane) backups. I have mine disconnected from the stat, so the funaces only fire up during defrost, but I am in S Tx, and so far in the

6 years I have had them, they have always been able to keep up on HP alone, although we have not had a real cold winter for quite a while. The units are about 20 y/o-- they were takeouts that I installed here to get away from the expense of propane. Another thing you could do is install an outdoor thermostat to keep the aux heat from coming on when the temp is above a certain temperature-- usually around freezing- more or less. Larry
Reply to
lp13-30

Larry - that sounds like a plan. Are the wires clearly marked, in general? You are saying that that won't affect the defrost?

Reply to
dean

Dean, diconnecting the wire from the thermostat will not affect defrost. The wire controlling that comes from the outside unit straight to the air handler(inside unit). The wire for that in the unit itself is Black on a Trane, but the installers may or may not have hooked up a black wire to it to run into the inside. They may have used a white, though itis possible that they used any color they chose. The wire from the thermostat to the air handler that turms the aux heat on should be white. If you can figure out which set of wires go to the stat, and which goes outside, you can disconnect the wire at the air handler if that would be easier for you than disconnecting it at the thermostat. Hope this helps Good luck Larry

Reply to
lp13-30

Larry, thanks for the advice, I will add a small over-ride switch to the thermostat.

Cheers,

Dean

Reply to
dean