I remember someone asked if I could post what I found when I opening the boxes up and checked the wiring.

Before I started I figured out the counter top stove is on the same circuit.

2 single pole 30amp/30amp [Breaker] ? ?6 ? 12 30amp/30amp 16 [box]???????[fuse box]?????????[Oven] ? ? 12 30amp/30amp ?? ??????????[fuse box]?????????[Stove Top]

I doubt the line drawing will be legible, so I will try to explain.

Both single pole breakers were 30amp (one of the switches was chipped hence why my dad read 50amp on one.

The cable leaving the box was 6 gauge 4 wire.

when I opened the box under the oven I found 2 30 amp fuses and a 15 amp fuse. The wires coming into the box were 12 gauge 4 wire so I knew there had to be a box in the basement under the drop ceiling.

The old oven had 5 wires coming out and used the 15 amp fuse to protect the clock etc. The new oven only has 4 wires.

The box under the drop ceiling split the 6 gauge into 2 12 gauge runs one to the box under the oven and one under the stove top.

I did not check the gauge of the wire into the stove top but the wire that came with the oven is 16 gauge.

I replaced the two single 30amp breakers with a double pole 40amp.

I left the existing box in place and connected the new oven to the 30amp fuses and took out the 15amp fuse.

Reply to
Ned Flanders
Loading thread data ...

Other than the fuses, that sounds like a kitchen appliance tap circuit. Typically the two cooking devices split out of a junction box, off one feeder. The feeder can't be larger than 50 amps and the taps can't be smaller than # 12

>
Reply to
RBM

box]=E2=95=90=E2=95=90=E2=95=90=E2=95=90=E2=95=90=E2=95=90=E2=95=90=E2=95= =90=E2=95=90[Oven]

=90=E2=95=90=E2=95=90=E2=95=90[fuse box]=E2=95=90=E2=95=90=E2=95=90=E2=95= =90=E2=95=90=E2=95=90=E2=95=90=E2=95=90=E2=95=90[Stove Top]

16 gauge to feed a multikilowatt oven? My garage extension cords are 16 gauge. Something does not compute here.
Reply to
hrhofmann

Top]

I was as surprised as you... but I would hope Frigidaire knows what they were doing?

The old oven (Frigidaire) had thinner gauge wire then the new one - well all but the white neutral wire on the old oven. It was also 16 gauge.

Provided I am reading the gauge right?

14 solid copper = 16 stranded copper.
Reply to
Ned Flanders

Appliance wiring house wiring. The NEC doesn't apply.

Reply to
krw

The Nec does apply when tapping two appliances off of one feeder. The conductor leads furnished with the appliance must be a minimum of 20 amp

Reply to
RBM

Does it say what gauge those 20A leads must be?

Reply to
krw

No, just that it must be 20 amp, which leads me to believe that whatever gauge that wire is, probably asbestos covered, is rated for at least 20 amps

Reply to
RBM

It is *very* unlikely to be asbestos covered. It's not tightly enclosed, like Romex might be, so the temperature rise won't be as bad. All they need is a little engineering to verify that the wire won't melt (and convince UL, or similar).