They make them, although the 20A duplex 240V devices are expensive and not very common. But you can probably get a 15A 240V duplex outlet (has
2 horizontal slots plus a ground) at Home Depot or Ace Hardware for less than $10.
They make them, although the 20A duplex 240V devices are expensive and not very common. But you can probably get a 15A 240V duplex outlet (has
2 horizontal slots plus a ground) at Home Depot or Ace Hardware for less than $10.
Thank you for your well informed opinion. Just today I blew circuit breakers in the garage and kitchen due to running some stuff like a heater and a compressor. I think that I will splurge and install a real subpanel in the garage, and then a few outlets, 110 and
220v. This subpanel should also be protected by circuit breaker at the main panel, is that right? i
Yep, like you and Tom are suggesting, I will install a subpanel.
i
Yes but the sub panel will not need a main breaker because the breaker that protects the feeder circuit that supplies it fulfills that function.
-- Tom H
Yes and no. No in that the breaker at the main panel protects the cable(s) running to the sub panel, not the panel, or its circuits, but just that cable run feeding it.
Yes, in that it will have the effect of a shut off for the sub panel, but that isn't its intent.
You don't need a breaker that shuts off the whole sub-panel, in addition, you can have only the breakers you need for circuits.
HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.