Service panel upgrade question

The reason you can't bring all your nm cables into your box through one large connector is potential heat at that point (thats the theroy).

A common safe practice is to use 3/4 connectors and to limit each connector to 2 or 3 nm cables each.

An increase in your service size precludes a larger ground wire. Your existing ground is probably adequate,but your inspector may or may not call you on this.

Reply to
twiedeman
Loading thread data ...

I would like to upgrade a 1987-vintage 125A combination meter main service entrance panel to 200A. The existing panel is a semi-flush mount set into stucco, underground service, I'd like to replace it entirely with a semi- flush or surface moount box.

While pawing through the 1999 NEC (the one the county inspects to) I found that 373-5(c) no longer allows the arrangement in the current box, all of the NM cables coming in through a single opening with a bushing in the back of the box.

So two questions, please.

First, what is the preferred method for bringing NM loads into a box like this? 20 or so individual cable clamps seems bad, and I don't get how the exception for one or more 18" conduits into the top of the panel is supposed to work.

Second, can the existing ground wires (embedded in the stucco) be disconnected from the old panel and re-used, or will I need to replace them with new grounds?

Thanks for any guidance,

John

Reply to
John Lowery

I can't answer the questions posed but, I have a question for you on this. Do you have 200 amp service from the pole to your house? The reason that I ask is this. We had 200 amp service installed in our house (built in the

60's) and the wiring from the pole, the mast where the service is attached to the house, the meter and the panel all had to be replaced regardless of condition to handle the 200 amp service.

This was in Ontario, Canada so it may not apply to you.

Reply to
Ron

If you are required to upgrade tour ground, you may also be required to bond old and new grounds together. It probably is a sensible thing to do.

Square D QO series are the favored choices in our area. Opinion here is that they are easier to work with. YMMV.

Joe

Reply to
Joe Bobst

I'm working off the 2002 code as I don't have a 1999 code. Your talking about Stovepiping, it's fairly easy to do . You mount your surface mount panel then attach your raceways through knockouts on the top. When doing this, most people run a large conduit such as 2" and run all the cables through it. This is a easy way to run the cables when the box is mounted to a concrete wall. I prefer to build a wood backer and individually clamp each cable. You mentioned it was a semi-surface mount, you would have to run it through your inspector before trying this. Chances are you have a 8 ga. copper ground. You will need to up this to 6 ga. for your connections to your ground rod.

Nate

Reply to
Nate Weber

Your local inspector may allow you to circumvent this requirement because the cables are fished in the wall. The wiring method used for your existing panel isn't uncommon for that situation (at least in my area). If, for some reason he doesn't allow it, just ask him what he recommends as a solution. See below.

Your ground wires are probably too small......they need to be at least a #4 for a 200 amp service. Plus a portion of it (6") needs to be exposed for connecting telephone and cable TV grounds.

When building an electric service one should try to contact the electrical inspector who will be doing the actual inspection to get any questions answered. While you have him/her on the line, ask him if the Power Company has any requirements over and above the 1999 NEC......as some will. Most power companies have a manual that is called "Standard Electrical Service Requirements" (or similar title). Contact the Power Co. Engineering Dept. and tell them that you are trying to obtain a drawing/diagram for a "typical residential underground 200 amp service". They may be able to fax it to you. The drawing will show meter base mounting heights, what kind of meter base to use, clearances, grounding, grounding wire sizes, etc. As an example, my area (actually the whole State) is under the 1999 NEC, however, the Power Co. requires lightning arrestors (these are not required by the

1999 NEC) plus a few other changes not required by the 1999 NEC. The Power Co. has the final say and you _won't_ get hooked up until you meet their requirements also. Fortunately, there is usually good coordination between the Power Co. and the local electrical inspectors, so the inspector will be well aware of these additional requirements (if any).
Reply to
volts500

"volts500" wrote in news:VTXsb.108774$ snipped-for-privacy@twister.tampabay.rr.com:

I do have the local power company service requirements manual, and they don't have much in the way of additional requirements beyond NEC 99 and EUSERC-approved panels.

I'll definitely get in touch with the inspector before starting.

Many thanks to everyone who took the time to reply.

John

Reply to
John Lowery

"Ron" wrote in news:DNLsb.106323$ snipped-for-privacy@nnrp1.uunet.ca:

We have underground service, and a combined meter and distribution service panel, so it'll be replaced as a unit. I'll need to trench out to the service pad (about 30 feet) to allow the installation of the new feed.

Thanks, John

Reply to
John Lowery