Romex wire hookup

Yes, this is the main service panel. There are 2 buss bars running vertically down both sides of the box. There are BOTH white and bare wire's hooked to EACH bar. Hence, my confusion.

Reply to
Ed Mc
Loading thread data ...

Since it is a main and not a subpanel, that is correct -- both white and bare wires can be (and usually are) connected to each bar.

RBM wrote above saying the same thing:

"If it is the main service panel, the neutrals and grounds go on the same buss. If it is a sub-panel, there will be separate neutral bars and equipment ground bars."

And, Nate Nagel wrote that that is correct. Others probably did too, but I'd have to go back and read all the messages again to check.

But, again, what you wrote ("There are BOTH white and bare wire's hooked to EACH bar") is correct for a main panel.

et.tnT

Reply to
Jay-T

Depends where in the world he is. In Canada, there are 2 busses - one ground (for bare wire) and one neutral (for white wire) - bonded for main panel and not bonded for sub. - and code requires the neutral and the safety ground to be installed on their correct Buss.

>
Reply to
clare

snipped-for-privacy@snyder.on.ca wrote: ...

I'm virtually positive that's what US NEC says, too...

Even if not, it is, imo, poor practice to mix the two.

Reply to
dpb

Reply to
RBM

Reply to
RBM

Yup, the main lugs and the main breaker are in a separate section of the panel. Removing the cover to work on the breakers doesn't expose them (does expose the hot bars the breakers grab onto, of course.) And the neutral and ground bars are separate, connected in one place with a tie that's removable for subpanel use. And all the screws are Robertson. This one's typical; see in the right photo how the top part is still covered:

formatting link
(Homedepot.ca). See also how it's more expensive than what you get in the US even with the dollar at over 95 cents.

But I gotta tell ya, the milk in bags thing is a losing proposition. They spill, they flop around in the fridge, they dribble down into the pitcher...dumb idea.

Chip C Toronto

Chip, the panel that you linked to, has 2 equipment ground only busses. Is it Canadian code that a service panel must have them, is this something new, and can you or could you ever, install equipment grounds on the neutral buss, as we do in the US?

Reply to
RBM

If it does say that, it's a new addition since the installation of the panel in my house (and/or whoever did it didn't do it to code - but I would ASSume that one would have pulled a permit for a panel replacement...)

I agree that it seems like a good idea, I just haven't seen it done.

I believe there's something in there about not putting more than one neutral wire under a single screw, though? You can have more than one ground under a screw, just no more than the connection is rated for (e.g. it might be 3x 14AWG, 2x12AWG etc.) but only one neutral. I assume this is to remove the possibility of opening a neutral on an energized circuit while trying to service a different circuit.

Yes, I am in the YooEss. Not an electrician, but pretty handy. I do try to "do things right" but don't pretend to know everything about code.

nate

Reply to
Nate Nagel

RBM wrote: ...

Any I've seen in the recent past have two. The service-only panels have the neutral buss also grounded to the cabinet but still have two busbars.

Even my ancient FPE stuff was built that way...

--

Reply to
dpb

There are a number of manufacturers, each makes a pile of panel styles, with a multitude of neutral/ground buss arrangements. In the US , regardless of the buss arrangements, if they are attached together, attached to the service neutral, and the grounding electrode system, you can attach both neutrals and grounds to them. There are some panels made, which Bud made reference to, that have an equipment grounding "only" buss. This buss is attached to the frame of the panel only, and not to the service neutral conductor except via the steel of the cabinet. It may be that in Canada, this type of arrangement is what's required by code

Reply to
RBM