On 07/22/2015 9:44 PM, dpb wrote:
...

OBTW, you could put a remote disconnect and then run #10 to the actual connections. It (the wiring, not the motor that has its own) can be protected at the local with just a disconnect remote/near the motor if it's sized for the ampacity of the load which 10 will carry; you just need the larger in this case because it's a motor to avoid the voltage drop for startup.
--



Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

The motor is 1 HP. If wired for 115 volts it takes 23 amps and if 230 volts it takes 6.5 amps.
If ran on 60 hz it runs at 1723 rpm and if 50 hz 1425 rpm.
It has a thermal switch inside so if it gets too hot it will stop and when it cools down it can be restarted.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Tuesday, July 21, 2015 at 9:07:11 PM UTC-4, dpb wrote:

Yes, it's definitely a dual voltage motor. Yes, you are correct in that my voltage drop calculation is incorrect (used the wrong current) and I just redid and found only a 4.5volt drop (2% drop). Yes, I plan on going with #10.
Thank you, evereyone, VERY much for the advice, all of which was well-referenced and thought out.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

#10 would probably suffice for the running load, but the starting load will be much greater. I would go with #8 copper wire. You should contact the manufacturer and see what they recommend for a wire size and a breaker.
Check out article 430
John Grabowski http://www.MrElectrician.TV
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload