outdoor wiring question

I want to run two lines from my basement to a second-floor bedroom. One will be 12-2 non-metallic cable, the other cat 5 wire for an internet connection. For part of the run, the wires will run along the outside wall of the house. The run will be 10 feet horizontal, a 90-degree turn, another 10 feet horizontal, a 90 degree turn, 10 feet vertical. I want to enclose the wires...my question is, can I use pvc pipe? Or must I use emt? and what size would be appropriate. Thanks!

Reply to
eag111
Loading thread data ...

PVC can be used outside when not subject to physical damage AND rated for the installation. I am not aware of any PVC that is rated to be exposed to the sun. There were some companies that made 2 inch PVC risers for residential. I have not see those for a long time.

If you live in sun country PVC even painted will not hold up for very long.

You do know that the cat 5 cable needs to have a 300 volt rated insulation to be run in the same conduit.

The insulation on romex/ non-metallic cable is not rated for running in conduit.

I am not sure if wire mold can be subjected to the elements. If it can it might be a thought.

Reply to
SQLit

---------------------------snipped

Nonmetallic-Sheathed Cables UL 719

1 Scope 1.1 These requirements cover nonmetallic-sheathed cables containing 2 - 4 thermoplastic-insulated circuit conductors with or without a grounding conductor in the constructions indicated in Table 1.1. These cables are intended for use in accordance with Article 334 and other applicable parts of the National Electrical Code (NEC) , ANSI/NFPA 70. Type NMC cable is for use in dry, moist, damp, and corrosive locations, and Type NM cable is for use in normally dry locations. Both types carry the suffix letter "-B" to designate the use of conductors with 90°C insulation.

The best part of the United States is the ability to speak your mind. Even if you have a dissenting opinion.

Reading Article 334 I will concede that there is nothing that says NM, NMC, or NMS and not be run in conduit. There are several references to dry, moist , damp and other locations. There is nothing that says it can be installed in a wet location. I consider outside a wet location.

Reply to
SQLit

SQLit wrote: ....

Buy inside a terminated-on-both-ends conduit is a dry location...

Reply to
Duane Bozarth

PVC electrical conduit. Half-inch trade size meets Code, but it'll be a bitch pulling the Romex cable through. Go bigger: 3/4" or 1". There's not much cost difference, and you'll be glad you did.

You need a separate conduit for the CAT5 cable. 1/2" will be fine there.

PVC electrical conduit is. PVC water pipe is not.

You misspelled "can't be run in the same conduit".

False. Why you continue to say this, after your error has been pointed out to you many times, is a mystery to me. There is *nothing* in the NEC that prohibits use of NM cable in conduit.

Dry locations only.

Reply to
Doug Miller

Hi, Instead of CAT 5, how about going wireless? Tony

Reply to
Tony Hwang