# of wires per jucntion box -- includes the ground wire?

As an example, I am looking at a ceiling fan box that says that it is rated for up to five #12 wires.

Does that include the bare ground wires that will be going into the box, or is it just the conducting wires (such as the black and white wires)?

Reply to
Len56
Loading thread data ...

Yes. (But... :) )

You don't have to count wires under #14 from a fixture to wires in the box.

A wire originating in and terminating in the same box (ground from green terminal of an outlet to box ground, for example) doesn't count.

A wire running thru a box w/o splice or tap counts as only one wire (from which one can deduce the answer to the original question, btw).

And, of course, the limit for #14 would be higher than for #12 (probably by one altho I didn't check tables).

There are other conditions/adjustments but those are the highlights that are probably the pertinent ones for the application.

Reply to
dpb

Each circuit conductor entering the box is counted once. All the EGCs (ground wires) together count only once.

Cheers, Wayne

Reply to
Wayne Whitney

Reply to
Len56

all the bares count as one.

Reply to
Steve Barker

Note the distinction: circuit conductors are counted. Fixture conductors (the leads to a lamp, for example) are not.

Also:

- a conductor that both enters and leaves the box, without being spliced, is counted only once

- any conductor, no part of which leaves the box, is not counted at all.

Reply to
Doug Miller

Not quite. The rule is "no part of which leaves the box". I grant that it would be highly unusual, perhaps unique, for a conductor to leave the box in which it originates and return and be terminated in that same box, but any such hypothetical conductor that might exist must be counted as two.

Not necessarily. The OP said the box is marked for up to five #12 conductors, which means that its capacity is at least 5 * 2.25 cubic inches per conductor, or 11.25 cubic inches -- but that is *not* big enough for six #14s at 2.00 cubic inches each.

Reply to
Doug Miller

*Just to clarify the above according to 314.16(B)(1): "Each loop or coil of unbroken conductor not less than twice the minimum length required for free conductors in 300.14 shall be counted twice".
Reply to
John Grabowski