When I asked a few weeks ago, I was a bit confused but now I have done more research and done my own load calculation. Here it is: would one of you more experienced souls check this to see that I have done it correclty. I'm sure the math is fine, I mean the assumptions and method.
Questions: The main area I am still questioning is about the number of circuits considered to be applicance circuits that are subject to the 1500VA rating rather than just being general lighting circuits subject to 3VA/SF (should I have included the garage ckt). Also in adding an additional general lighting circuit, I do not need to increase the load requirement. Right? My last question is about the dishwasher. Code says it needs to be seperate from disposal but can it be part of ckt 7 or do I need a dedicated 20A new branch ckt.
Calculations follow:
Existing 100A service CKT Amps Location Load
1 15A Exterior and Interior lighting l1 lamps on 6 switches 2 50A/240V Range 1 hard wired box 3 30A/240V Drier 1 receptacle 4 20A All bedrooms and bathrooms 11 Receptacles, 3 switches 5 20A Living Room, Middle BR 5 Receptacle, 1 ceiling fix, 2 switches 6 20A Refrigerator, microwave, sink 3 receptacles 7 20A Kitchen counter, wall, 2 receptacles 8 20A Garage, attic fan, patio 4 receptacles, 1 switch 9 20A Disposal 1 receptacle , 1 switch 10 20A Back Yard Receptacle and Shed 3 receptacles, 2 lamps, 1 switch (GFCI)NEC 220-31 Calculation of Loads Service = 100A x 240V = 24000VA (Main) Other Loads
1000 SF x 3VA/SF = 3000VA (Ckt. 1, 4, 5, 10) Appliance Ckt 3x1500VA = 4500VA (Ckt. 6, 7, 8) Range = 8000VA (Ckt. 2) Dryer = 5000VA (Ckt. 3) Disposal = 1000VA (Ckt. 9) subtotal = 21500VAFirst 8000VA at 100% = 8000VA Remainder at 40% (13500VA) = 5400VA
Total loads = 13400VA /240V = 55A
New Loads Dishwasher = 1200VA (Ckt. 7) Lighting Circuit = included (Ckt. 11) Steam Generator = 8500VA (Ckt. 12) New Loads = 11200VA
- Original loads (21500VA) = 32700VA
First 8000VA at 100% = 8000VA Remainder at 40% (24700VA) = 9880VA
Total loads = 17880VA /240V = 75A