Is this the best type wire/method to use???

Hi all,

I'm running electric to a new shop building underground for about

185 feet. I'm considering using aluminum tri-plex #4 or #6 inside 1" PVC buried about 2 feet. I'll be running a 120V air compressor, an arc welder, and a 120V window A/C but not all at the same time. The reason I'm looking at the aluminum tri-plex is the cost which is .70/.85 cents a foot in my area. Is this the best and least expensive way to do this job ? I'm doing it myself so I'm not worried about code but I will have sufficient breakers on both ends. Any suggestions/ideas please ?

J SW Georgia

Reply to
Joey
Loading thread data ...

Hey Joey,

If I were you, I'd definetly go for the copper, as for amp draw, #6 awg is usually good for

60 amps at 100 ft and #4 is 80 amps at 100 ft, BUT for aluminum #6 is only good for 40 amps at 100 ft and #4 is 60 amps, so you see you loose 20 amps by using aluminum.

The air compressor and 120v window unit won't be a problem, but your aluminum might get pretty hot with the welder after running awhile, it happened to me once, got real hot real fast, even with a breaker.

mrkool

Reply to
mrkool

I'm not sure if you want the best way to do the job or the cheapest.

From my own experiences repairing underground aluminum conductors, I would never use it that way even in conduit. Copper is the way to go underground. I suggest that you use a larger conduit such as 11/4" to make it easier to pull. It might be cheaper to buy individual conductors instead of the triplex. It is a long run so you should go with the larger size wire. For a 220 volt service you will need 4 conductors. The grounding conductor can be smaller based on the size of the other conductors.

Since you are doing it yourself it is all the more reason to pull a permit and have the work inspected.

John Grabowski

formatting link

Reply to
John Grabowski

Check the price of #4 (or #3) aluminum UF cable; individual conductors rather than triplex. I'd be tempted to direct-bury that with a bare #6 solid copper wire for the ground. I don't know if you can double-up the neutral and ground wire that way or if you'd need 4 conductors. (For overhead wiring you'd only need three, but underground is probably different.)

If you use triplex or quadplex cable, make sure it is rated for underground use and isn't just for overhead wiring.

BTW, overhead wiring is a PITA, so I don't recommend that method.

See if you can rewire the air compressor for 240V; some of them are convertible. It will be a lot happier on 240V.

Bob

Reply to
zxcvbob

It's your house so do as you please but we would need to know what the motor size is on your air compressor, the name plate current draw of your arc welder, and the amperage draw of your window air conditioner in order to answer your question.

-- Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison

Reply to
Member TPVFD

Reply to
Sacramento Dave

I too, have no way to tell from the info you provide, what size feeder you need, but also agree that copper would be a better choice. Keep in mind the conductor insulation must be approved for "wet" locations like THWN. Most insulation has multiple ratings, however in larger sizes you can still find straight THHN wire which is not rated for wet locations

Reply to
RBM

According to Joey :

When we wired our detached garage (100A, 120' worth of sub feed), it would have cost about $700 in copper versus $300-ish in Al.

#3 Al triplex versus #4 Cu NMW (aka US UF).

In our area (Canadian codes), you can direct bury NMW (no conduit or other protection) as long as it's >24" underground (goes to >30" under driveways/roads). You can subtract 6" from the depth if you put it in CSA-rated PVC tubing. (I don't think the NEC permits PVC tubing of any kind, has to be real conduit).

We used a PVC sleeve under the driveway, but not under other parts because the trench was 24" thruout.

Given the price difference, we went with the aluminum. Haven't regretted it. But it does have to be carefully done exactly to code (grease etc).

Reply to
Chris Lewis

I am an electrician (retired)

But most areas do not even allow aluminum to be used any more. (too many corrosion problems when terminations/joints are not done properly)

Also aluminum wires have to be heavier than copper for the same load, so #6 aluminum can be #8 in copper, you may find the prices are about the same in the end

Copper wiring is still the best.

Gauge of wire you need depends on the loads you will be drawing, and also local codes , but it's always a good idea to figure out what you need then go up one size (you may decide next year to buy a heavier welder)

The codes are there for a reason, follow them (or better them) even if you decide to do it without an inspection/permit.

As with the other posts I agree that you can pull individual cables and save a few bucks over the cost of triplex. You can easily go up a size or two more than you need on the conduit to make it easier to pull, and provide room for more wires later if you need them

Reply to
Amun

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.