Interconnected Smoke Alarms -- Options/Wiring -- Wireless?

to interconnect the alarms, you need a third wire run between the alarms. The third wire is usually in the 14/3 i,e usually the "red" wire. It does not matter how the wire is routed, it does not have to be directly between the alarms, as long as it gets connected.

The hard part is that you probably have 14/2 running to the alarms and that would have to be replaced with 14/3. The third wires from each alarm could then be connected together wherever they meet. i.e in the breaker panel.

M
Reply to
makolber
Loading thread data ...

If I understand what you mean, it is not correct. The alarms now are individual battery operated alarms that are not connected to each other. So there is no 14/2 running to them or between them. 14/2 would go from the panel to the first detector, so there would be no third red wire in the panel to connect to anything. From the first detector to all of the other detectors, there would be 14/3 wire. And those red wires would all be connected to re, the black wires connected to black, and the white wires connected to white.

Reply to
TomR

Sounds like you have it right. IDK how you can figure out which detectors are good ones. I have a house with ones that are about

8 years old, that are both AC powered and battery powered. They are a real pain in the ass. You would think that with AC, the battery would only be used if AC drops out. But the damn things start beeping for a battery change in less than a year and with a whole bunch of them, it gets annoying real fast. If it were up to me, I'd get ones that are AC only, but that probably isn't sufficient in many places today.
Reply to
trader_4

when installing connected smoke and presumably co2 detectors. put all of them on the same breaker!!!

HOWEVER not all by themselves, so someone cant turn off one breaker to silence them. then forget about it being off.

put a often used light on that breaker, like a kitchen light, so its not forgotten if its off.

Reply to
bob haller

I would be cautious about this strategy.

You would think doing more would be better, but when you do that you have t o meet complete code requirements for the extra, even if the extra isn't re quired. That exposes you to all sorts of liabilities and may fail an inspe ction. Since this is government work, they will understand meeting the min imum requirement, and they will be anal about meeting EVERY spec if you do more than the minimum.

I looked at that recommended wiring diagram. That absolutely would not mee t code in any of my projects. (but we only do commercial where I work) A break at one alarm disables everything downstream. We are required to do r edundant loops so one failure is just that, a single failure.

Now, with your single wire, when it breaks, how are you going to find and f ix it?

Reply to
TimR

to meet complete code requirements for the extra, even if the extra isn't required. That exposes you to all sorts of liabilities and may fail an ins pection. Since this is government work, they will understand meeting the m inimum requirement, and they will be anal about meeting EVERY spec if you d o more than the minimum.

eet code in any of my projects. (but we only do commercial where I work) A break at one alarm disables everything downstream. We are required to do redundant loops so one failure is just that, a single failure.

I guess the same way that people find and fix a broken interconnect wire in the many millions of homes that have been wired that way now for decades. Or the same way you find and fix any open connection in any circuit, for that matter.

Reply to
trader_4

- Yes

I have

Wireless means wireless. I noticed that my local electrical supply company is now carrying wireless smoke alarms. I had a customer who wanted to add smoke alarms to an existing wired system. The fire inspector told him it was acceptable to switch to a wireless system.

John Grabowski

formatting link

Reply to
John G

With a couple of exceptions, though.

For one thing this wire isn't one branch circuit in a room or couple of rooms. It extends across the entire house, everywhere there's an alarm.

Secondly, we're not talking a porch light that doesn't come on - we're talking a life safety device, and in a rental where it's required to work.

Third, you probably won't know it broke until the house burns down - is there any kind of supervisory circuit on these?

Reply to
TimR

So, because it's longer, now it can't be debugged using the same methods you would on any other circuit? There aren't lights, receptacles at the far end of your house, where the circuit runs the length of the house?

If the interconnect wire is broken, the alarms still work individually. If the AC power connection is broken, you have the exact same vulnerability that you do with any smoke detector that's powered by AC only. The ones here in my house are like that, on one breaker. And if you want increased reliability, there are dual AC and battery operated alarms, which are required by code now in some places.

You're trying to impose requirements way beyond those that likely exist. Is there any supervisory circuit in the many millions of smoke detectors sold at HD, installed in millions of houses, including rentals? There is no code requirement here in NJ for supervisory circuits in a single family rental home. I doubt there is where he lives either. I agree he should see what local code is and meet it, I'v said that from the beginning. But to throw a lot of FUD into it about some alleged inherent reliability problem with interconnected alarms in widespread use doesn't make sense to me. In the overwhelming number of deaths from fire, the smoke detectors didn't work not because of some interconnect problem, loss of AC power, etc. They didn't work because they had dead batteries, no batteries, or there was no smoke detector at all.

And it sounds like his issue with the govt, is probably section 8. They require that a rental property meet very basic requirements, if you can get a CO, then it almost certainly is Section 8 acceptable. They will look for the existence of required smoke detectors, but they aren't going to do an electrical inspection of how they are wired and they probably don't care whether they are interconnected or not either.

Reply to
trader_4

No. This is where you are 100% wrong.

Well, you are right from the common sense view.

But not from the regulatory view. You build a safety system that was bette r than required, but then you were required to have it completely functiona l. You are better off to not have it at all than to have it and not have i t work exactly as designed. That may not make sense but that's the way cod e works.

Reply to
TimR

I'm 100% right. I said if the interconnect wire is broken, the alarms still work individually. THAT is 100% true.

What regulatory view changes that they still operate? None.

You build a safety system that was better than required, but then you were required to have it completely functional. You are better off to not have it at all than to have it and not have it work exactly as designed. That may not make sense but that's the way code works.

If he puts in a system with an interconnect wire, ie the common type that is already installed, used, sold at HD, etc, it may or not be better than what code requires. Code may not require it to be interconnect ed. But if he puts it in, it works. It meets code. If a unit fails at some point in the future, he replaces it. If the interconnect wire fails, which is extremely unlikely, he fixes that. I don't see what the big issue is. I have had interconnected smoke detectors in 3 homes now. They work. They are widely used, so why all the FUD?

FUD:

"You would think doing more would be better, but when you do that you have to meet complete code requirements for the extra, even if the extra isn't r equired. That exposes you to all sorts of liabilities and may fail an insp ection. "

All he's talking about doing is putting in an interconnected smoke detector system in a single family house. These are widely used, are code compliant, all across most of America. What are these "liabilitie s"?

" S " It is a detached single family home, but the family that lives there has some government funding which means that the home itself is inspected by a representative from that funding source/agency. They "recommended", but are not "requiring" an interconnected alarm system with a control panel etc. "

So, this sounds like Section 8. And they have told him that they don't have any special requirements that he has to meet. Good grief.

"I looked at that recommended wiring diagram. That absolutely would not me et code in any of my projects. (but we only do commercial where I work"

Well duh. He doesn't have to meet commercial requirements or rewuirements for a rocket fuel factory either. He only has to meet whatever the local code requirements are for single family rental properties. And he can fill us in, but I bet if he looks up the local fire code, basic interconnected smoke detectors like you see across America are compliant. They are here in NJ. End of story.

Reply to
trader_4

Thanks. I think my plan is going to be to get the ones that are AC powered with a battery back-up, but ones where the battery is a built-in 10-year (allegedly) lithium battery. Also, I want them all to have a "Hush Button" feature to silence the alarm triggered by a known cause such as cooking or shower mist/"steam". I am not sure, but I think the battery back-up feature in AC powered detectors is either the code (in locations where interconnected alarms are required), or are at least recommended. I guess the theory is that if a fire is started by an electrical malfunction and/or arcing etc., which also causes the AC power to go out (what are the odds?), then the alarm system will still work with the battery back-up.

And, I think the detectors are supposed to be changed every 10 years anyway (especially CO detectors, I think), then changing the detectors when the lithium battery dies would make sense anyway. Yes, that costs more money, but that's okay with me. Also, in the promotional literature for the more expensive lithium battery back-up models, they claim that the increased cost is offset by not having to pay the cost of replacing regular 9-volt batteries every year for 10 years.

Reply to
TomR

Thanks. Good to know.

Reply to
TomR

I think a bigger factor would be that when the power goes out, a lot of people start using candles, fireplaces, wood stoves, etc with a higher potential of starting a fire.

I agree, that 10 year Lion sounds like a good idea, especially for a rental property so you don't have residents fooling around, changing batteries, etc.

Reply to
trader_4

In news: snipped-for-privacy@googlegroups.com, trader_4 typed:

I am not sure on what the best or easiest place for me to chime in on this aspect of the discussion is, but I'll start here.

1) TimR, I understand the points that you are making and I will explain why I know what you mean below. 2) trader_4, I also understand and agree with your point of view on this, with the only slight exception being that I have an and understanding of, and some experience with, the somewhat subtle point that I think that TimR is trying to make.

So, here it goes:

TimR, yes, what you are saying is probably correct in a commercial location/application. But, this is not a commercial location/application. And, no, the interconnected alarm system (if I do one, and whether hard-wired or wireless), would not be a "supervised" alarm system -- meaning no third party monitoring of the system, no power failure warning, etc.

Nevertheless, I do know what you mean about "mission creep", meaning that if I do decide to do a change, upgrade, or improvement of the current individual battery powered detectors alarm system, will that trigger some governmental oversight entity to then want to enforce an even more complex (even though not required) standard or "code" requirement? There are reasons why I know this, which I will explain shortly.

However, in the interim, I would like to throw in some additional information regarding my experience in this area. Completely unrelated to this present situation, I happen to personally own a 3-family residential rental property that I purchased maybe 8 years ago. It happens to be in New Jersey, which I am mentioning since trader_4 mentioned New Jersey code requirements. When I bought the 3-family residential rental property, it already had an interconnected 110-volt with battery back-up alarm system. That alarm system is on its own circuit with nothing else connected to it. And, it does not have an "alarm panel" and it is not a supervised or third party monitored system. It meets all of the current codes. One of the local codes for that system is that I have to have the system tested and an alarm certification done annually. So, I do know how such a system works and what the code requirements are for such a system. And, again, that is a residential, not a commercial, application. And, yes, if there were a break in any of the connections, including a break in the interconnected signaling wire, I would have to resolve that issue.

Now, back to the question of, if I decide to upgrade a system anywhere, will "they" try to tell me that my upgrade may have to go even further to a much more complex, supervised, system etc? I don't think so, but they may "recommend" that. In fact, that is what happened to me in this case.

I don't want to go into too many specific details here on a public forum, but I can say that I actually have 2 other single family homes that are "similarly situated" with the home that I am writing about now being one of the 3. All 3 have the same sort of "governmental funding" aspect to them with regard to the occupants of each home -- although the actual source and type is not Section 8. In the past, funding was made available to upgrade or make capital improvements to the first two of the homes (before the third home was purchased) about 10 years ago (or more). At that time, one of the upgrades that I decided to do was to have a supervised interconnected fire detection and alarm system installed in each of those two homes. It "seemed like a good idea at the time". But, now I regret having done that. It was overkill, unnecessary, and not a requirement for a single family home -- even a newly built single family home. It is a pain. It requires constant monitoring for a fee, it results in unnecessary false alarms or accidental alarms where the fire company has to respond, etc. And, of course, it requires monthly monitoring fees, alarm system maintenance, etc. And, since governmental funding helped pay for that system, (and even if it didn't), it would be a liability (in my opinion) if I now decided to remove or downgrade those two systems to just what the code requires if there were to be a fire at any time in the future in one of those homes.

Now, what has happened is that the same governmental funding entity that visits those first two homes (with the complete alarm systems in place), also visits the third property which was later purchased and which does not have the type of complex complete alarm system that the first two homes have. That's what apparently eventually led to the "recommendation" that this third home should have the complete complex alarm system installed -- even though it is not a code requirement.

So, for that reason, I have an understanding of the "no good deed goes unpunished" aspect of this situation, and the possibility that agreeing to do ANYTHING could prompt or trigger an expectation or request that EVERYTHING be done -- meaning the whole new complex complete (not required) type of alarm system.

Nevertheless, I am completely confident that if I do decide to just do the interconnected hardwired 110-volt alarm system with a battery back-up as a "compromise", I will not be subjected to any additional liability or risk for not having done a whole new complete complex alarm system. But, that is why I understand what you, TimR, are suggesting as a possible aspect of what could happen by my deciding to do something (anything) rather than nothing.

Reply to
TomR

Good point. Makes sense to me.

Yes, that's another reason why I would go with the built-in Lithium Ion battery versions.

Reply to
TomR

TomR, Yes, I think you understand the complexities of this.

My area manages 415 buildings, all of them multiple occupancy, all of them alarmed, many of them sprinkled. I know the pain of some well intentioned person deciding to go beyond the minimum and step into a quagmire of regulation and oversight.

Reply to
TimR

It would be interesting to see some case law on that. First the fact that govt subsidies are helping pay for the rent of some tenants that you may chose to rent to or not, is irrelevant. Whether anyone could prevail with a case against you for a situation where the work was legally done, inspected, up to required code, but arguably not as good as what was there before, I think is doubtful. If I have a rental property that had bars on the windows, I decide during a renovation that I don't want to replace them, code doesn't require them, if a subsequent renter sues me when the house is broken into, can they prevail? It meets code, they knew what was there or not there when they rented, etc. How about if there was a heated sidewalk, I decide to take that out, now a tenanat later falls and claims that as a reason? I replace one fire rated door with another, that while fully meeting code, isn't as fire resistant as the original? This would lead to all kinds of crazy suits. Code is there for a reason, it sets the minimum safety standards.

Again, what does the local code say? That is what is most relevant. Did you ask that govt rent subsidy inspector what happens if you upgrade it to an interconnected system, but not a monitored system? Did you ask them about wireless? THAT would seem to be more relevant than opinions here.

That's what I would think too, but I'm not talking to the fire marshal and the govt subsidy folks. I just objected to the huge dump of FUD, ie that you now would have an interconnect wire running the length of the house that for some reason can't be debugged if there is a problem, no redundancy for the system, etc. What you're proposing is in existence, code compliant in millions of single family rentals across the country. And it's an improvement over what's there. I don't think you should fear making an improvement that is code compliant, in widespread use, a good idea, increases the safety of your renters, etc over FUD.

Reply to
trader_4

I said nothing about monitoring. The word I used was supervised. Supervised is not monitored, they are two different things.

All the systems I put in are supervised. In the context of an alarm system, supervised means there is something that will detect a fault condition. A break in the line, an increase or decrease in resistance, etc., will trigger a warning.

Reply to
TimR

TimR,

Interesting. Thanks.

Since you mentioned sprinkler systems, my first thought is, "don't get me started on that one."

For exactly the same issue of not wanting to get myself caught up in a whole new quagmire of excessive regulation etc., I decided to forego an opportunity that I had to add a sprinkler system to one apartment while I was re-doing all of the plumbing. What happened was that in the 3-family residential rental that I mentioned earlier I was completely re-doing the bottom level apartment -- all new everything, completely gutted down to the bare walls and open ceiling and then back up, with all new electric, plumbing, etc. And, I actually took that opportunity to separate out the water supply for each of the 3 apartments. I changed it in a way that I can later just have 3 separate water meters easily installed if I want to, although I left it with just the one existing water meter for all 3 apartments. While doing that, I considered adding a sprinkler system to just that one apartment. Definitely not required, but I thought that it would be a nice safety feature to add since I could easily do that while doing the other work. But then I researched what types of regulations and testing requirements etc. come along with having a sprinkler system and decided that there was no way I was going to sign myself up for that. So, what could have been a nice safety feature just ended up not getting done. It just would not have been worth all of the future aggravation to go ahead with that idea.