i screwed up a thermostat install

hello everyone. i just installed a digital thermostat. while reading the instructions i missed the sentence telling me to label the wires. i know. i'm a moron. i assumed they were color coded (i.e. r=red, o=orange, w=white etc.). can this foul up be salvaged? i greatly appreciate your help.

Reply to
lodingi
Loading thread data ...

Clearly, you should have noted the color and letter terminal the wires were attached to on the old stat. You haven't mentioned what the thermostat is controlling, however at this point, you'll probably have to determine what each wire is attached to on the other end

Reply to
RBM

it is attached to a forced hot air oil furnace and a central a/c unit. how do i determine where each wire is attached?

Reply to
lodingi

On the old thermostat is there a jumper between terminals RC and RW?

Reply to
RBM

I'm sorry, I meant between RC and RH

Reply to
RBM

no there isn't a jumper. the old thermostat has five wires.

RH, G, Y, W, RC

the color of the wires are red, green, yellow, white & orange.

Reply to
lodingi

If there wasn't a jumper between RC and RH, you have a two transformer system. Two wires will operate the heat and three will operate the cool. The connections for heat are RH and W. If you touch the red and white wires together, see if the furnace fires up. If so, connect those two wires to the new stat rh and w. The green wire should go to the G terminal for the cooling fan and the yellow should go to Y for the a/c condenser, and hopefully the orange wire is the RC for the cooling. After connecting the two heat wires, just touch the orange to the green wire and see if the blower comes on. If so, I think were good

Reply to
RBM

So the ARE color coded? You could hope whoever did the installation followed conventions.

Reply to
CJT

I've used this to advantage in the past:

formatting link

Reply to
CJT

i wired it as you suggested. the blower is running and will not shut off. the new thermostat came out of the box with a jumper on the RH & RC terminals. i removed that jumper. should i have done so?

Reply to
lodingi

the thermostat says my home is at 69 degrees. i set the target temp at

68 degrees. maybe the blower is running to cool the house to 68? or maybe it's wired wrong? lol.
Reply to
lodingi

yes. when i touched the red & white wires together, the furnace kicked on.

Reply to
lodingi

Anything is possible. The blower could be on from the furnace (heat) or there should be a "fan" switch which could be turned on

Reply to
RBM

yes the blower turned on. the fan switch is on auto. the temp dropped to 67 and the furnace is on. i guess i'll wait and see if it turns off.

Reply to
lodingi

On the furnace, once it heats up and starts the fan, the fan runs independently of the thermostat and will continue until the thermostat is satisfied and the furnace cools down

Reply to
RBM

ok. what if the blower does not turn off?

Reply to
lodingi

take the green wire off of G and see if it stops

Reply to
RBM

will do. thank you very much for all your help.

Reply to
lodingi