Delta is still used quite a bit in small services where the customer also has a significant line to neutral load and prefers 240 L/L The power company likes it because they can do it with 2 transformers instead of 3. The down side is one of the legs ends up 208v to ground. The other 2 are just like a regular 120/240 because the system is grounded at the center tap of one of the transformers. Look at the transformers and you can tell.
3 p Wye with wye distributionTypically they use a larger transformer on the 120/240 pair to handle the L/N loads
Here is the only example of 240 center tapped delta I have ever seen with 3 transformers (behind the Hogs Breath in Key West)
The thing that attracted my attention was it still had one larger transformer. If you trace the connections you can see it
There is also a corner grounded delta but you usually only see it in places like sewer lift stations where there is no L/N load at all. The equipment will look exactly like single phase with 2 pole breakers and a white neutral but the voltages are 240 to ground on the ungrounded legs and 240 P to P